Results 1 to 13 of 14
    Midletown, Ohio
    Flotronic Monitor Software
    I'm looking for the illusive "flotronic monitor" software, I have 2 older flotronics machines that I recently took over the maintenance on and both units have dropped several compressors over the years. recently changed 2 compressors on 'b' circuit but can't get circuit restarted, changed out EXV, circuit board and sensors. I need to be able to look at what is really happening on the board. The "a" circuit is jumpered out because the oil pump died in the A1 compressor and I have to get the "b" circuit running before I can tear into the "A" circuit.
    As far as the machines go one is a 30GT170 and the other is a 30GB150 with 1500 step exv's.
    Any help will be greatly appreciated.
    JIM
    Dec 2000
    flourtown pa.
    Flowtronic program
    Send me your e-mail
    Greensboro, NC
    Smile Most common problems on 30GB/GT
    Hi,
    You probably have found out how smart the main board is. The board looks at the safties before start-up and will not allow start-up if the oil pressure switch is made on the lead compressor. Same goes if any of the other safties are jumped or in the wrong position before start-up. Which board did you replace? If it is the main board there is a jumper that must be installed on the new microprocessor that was not needed on the old board. There is a Carrier Bullitien covering that issue. Early flotronics had discharge gas temperature sensors that would open while running, contactors that had the shellac coating that is located between the iron surfaces sticking together causing the compressor to run after pumpdown until it burned up, sensors that would drift out a couple of degrees causing the superheat to go so low that the compressors would show no oil pressure due to liquid droplets in the oil.
    The configuration header from the main processor board must be installed on the new board....
    Hope this is helpful.
    flotronic monitor software
    Tomt
    I read that you might know where to get software for a 30gb. I've lost my copy and a coworker having problems with his chiller.
    Mooresville, North Carolina
    Believe it or not I work for carrier and can't seem to get this software.
    Refer all arguments to the wife, she's better at it.
    www.fairtax.org
    Mar 2006
    Pasadena, California
    30GB software
    I have the complete setup . Sofware runs on dos and you may need windows 98 or 2000 to run it. Also need a telabyte converter, transformer & some adapters to connect. Do a search on previous posts and you will find valuable info on this issue
    Dec 2006
    Middle Tennessee
    are they air cooled condensers?
    had a job in miami with 3-80 ton (30gt080's) chillers with air cooled condensers, tons of repairs were always needed
    i tried for years to get the owners to replace the condenser coils which were deteriorated due to salt air (close to the beach)
    finally after numerous compressor changeouts i got the ok to replace condenser coils
    replaced condenser coils using epoxy coated coils on all 3-80 tonners, those systems purred like kittens for years after that
    of course occasionally thermisters needed to be replaced.
    and i rebuilt a few mechanically faulty exv's which would cause lockouts due to slow stepping exv piston
    the way that carrier mounts the aircooled condenser coils allow for quick coil deterioration
    Southern New Jersey
    I have a customer with two 30GB100-650's serial 5090F43465. I really need that software if you help me out. These chillers are a bear without that software, I had it 15 years ago but lost it.
    Thanks, Bryan
    Dec 2000
    flourtown pa.
    flotronic
    need e-mail address. will not let me attach file
    Southern New Jersey
    Can I get the name of this software. I have service tool IV for DOS, but know nothing of a telabyte converter.
    www.fairtax.org
    Mar 2006
    Re 30GB Flotronic chiller
    I got this software from Carrier training dept. late 90s. Don't know the name. Its only good for the two digit flotronics with the 750 step EXVs. To interface with the GB processor you need the Telabyte converter.
    Flotronic software
    Just picked up an account with a couple flotronics. Can anyone help me out with that software. Ive tried gettting it from Carrier but they seemed lost. Any help would be appreciated. My email is tonys_baseball@yahoo.com.