Results 1 to 13 of 18
    Aug 2012
    Antelope,Ca
    White Rogers Ignition module
    I am working on a Payne m/n 584apw048080aa?g. I had an ignition problem with the orignal ignition module g770ngc-7. I installed a white rodgers module 50d50-843. followed the wiring diagram,added a burner ground, installed the green C chip. the ignitor sparks, lites pilot, main gas starts and shuts off pilot, no flame, main shuts off and restarts cycle. i have had this same problem with a Carrier furnace, tried a Robertshaw mod then a White Rodgers and both acted the same. is there something i am missing? is there a trick that is not in the paperwork?
    Southeastern Pa
    This is a commercial unit??
    Aug 2012
    Antelope,Ca
    it is being used on a commercial building
    Aug 2012
    Antelope,Ca
    the more i look, I am not finding this model # on line. the tag is bleached out and this # was written on unit above tag. could this be a 584apo?
    it is 3 phase
    Southeastern Pa
    Quote Originally Posted by RDorr92788 View Post
    When you say "on" a commercial building, do you mean this is a rooftop unit? Did you take a picture?
    pilot should remain energized in the sequence. You attempt checking/setting pressures?
    Sent from my SGH-T999 using Tapatalk 2
    Aug 2012
    Antelope,Ca
    yes this a gaspack rtu. no I did not get any pics. most likely i will be back there on Tue. I can snap a few then.
    Southeastern Pa
    Did you get a serial number?
    Aug 2012
    Antelope,Ca
    thats what i was thinking also, no i assumed pressures were ok. i will check it tue. assumtion is the mother of all ****ups.
    Aug 2012
    Antelope,Ca
    no serial available
    Southeastern Pa
    no serial available
    If you are facing the unit, is the flue over on the right hand end, where the gas line comes in, OR
    is it in the middle, with the gas line, right in front of you as you face the unit?
    Is the unit a light green color?
    Aug 2012
    Antelope,Ca
    facing the burner compartment , the flue and gas line come in at the right hand side near the corner. the inducer is at he bottom and the burners are on top. Tan
    Southeastern Pa
    Mercury switch for the pilot with three terminals?