    Faulty under-voltage relay? Is it possible to readjust at what voltage it drops out?

  2. #22
    Join Date
    Feb 2013
    Location
    Vancouver, BC
    Posts
    21
    Post Likes
    Thread Starter
    Well actually I didn't see it inside the drive. And voltage seems to be within the range (567-570V on 575V system)

  3. #23
    Join Date
    Mar 2012
    Location
    Southern CA
    Posts
    31
    Post Likes
    Quote Originally Posted by ddcbacnet View Post
    Faulty under-voltage relay? Is it possible to readjust at what voltage it drops out?
    In my case, the set-point (not even sure if it was adjustable, might have been) wasn't an issue. if i remember correctly, the relay was a NO contact in the control circuit portion of the drive. The coil went bad and it kept the drive off. I switched the connection to the NC terminal and presto it came to life (temp. fix of course)

  4. #24
    Join Date
    Dec 2012
    Location
    Lowell,MA
    Posts
    69
    Post Likes
    do you have o/m manuals? has pretty good troubleshooting chart at back of book or can call abb 800-help-365

  5. #25
    Join Date
    Feb 2013
    Location
    Vancouver, BC
    Posts
    21
    Post Likes
    Thread Starter
    Spoke to building engineer today. Speed drives are dead as a doornail and not subject to repair. It was caused by internal electronic failure within one of the components. Same component in all three drives. They did not mention which one.

    They say they will never turn them off ever again

    Lesson to learn: ALWAYS commission devices and systems you are about to upgrade.

  6. #26
    Join Date
    Dec 2011
    Location
    Fort Worth, TX
    Posts
    78
    Post Likes
    I have seen where someone accidentally hits a low voltage wire on a high voltage something (24volt wire hits a 277 volt leg) and instantly everything on that 24 volt circuit (safety or control) will never work again. Sometimes it is visible with small black arcing sports and sometimes not.

  7. #27
    Join Date
    Mar 2013
    Location
    Cincinnati, Ohio
    Posts
    17
    Post Likes
    I don't think that in my case the displays stayed off...just that the drives would not run...but I could be misremembering. If you have Eclipse bypasses you have to have the proper profile on the drive or nothing will work....on a new drive there is a paper attached to the thing - on old ones, who knows... Anyway, just a thought, and since the ABB man said it was electronic failure it probably isn't even relevant!

  8. #28
    Join Date
    Feb 2013
    Location
    Vancouver, BC
    Posts
    21
    Post Likes
    Thread Starter
    I found energized shield on one of FLNs. It measures 14VDC to ground(O.o WTF?).
    New VFDs detect insufficient grounding/network disturbances.

    I am trying to find out if poorly wired FLN could cause me all that head-ache.

  9. #29
    Join Date
    Dec 2011
    Location
    Fort Worth, TX
    Posts
    78
    Post Likes
    Quote Originally Posted by ddcbacnet View Post
    I found energized shield on one of FLNs. It measures 14VDC to ground(O.o WTF?).
    New VFDs detect insufficient grounding/network disturbances.

    I am trying to find out if poorly wired FLN could cause me all that head-ache.
    If you are controlling through comm it sure can. Otherwise no.

  10. #30
    Join Date
    Dec 2012
    Location
    Lowell,MA
    Posts
    69
    Post Likes
    have worked with a number of these and have never had that happen to me until i read this post, then the other day while starting up a unit, i shut the unit down,turned around and display was dead,have multiple fans so i took keypad from another and it was blank on this drive too, went and got a patch cable (just for kicks) and display lit up, anyway found coupler between drive and keypad had junk in it shorting it, was able to clear out and all is good again.

  11. #31
    Join Date
    Dec 2011
    Location
    Fort Worth, TX
    Posts
    78
    Post Likes
    Quote Originally Posted by Mike Doran View Post
    have worked with a number of these and have never had that happen to me until i read this post, then the other day while starting up a unit, i shut the unit down,turned around and display was dead,have multiple fans so i took keypad from another and it was blank on this drive too, went and got a patch cable (just for kicks) and display lit up, anyway found coupler between drive and keypad had junk in it shorting it, was able to clear out and all is good again.
    Good job! Good to know

  12. #32
    Join Date
    Feb 2016
    Posts
    1
    Post Likes
    well im sort of having the same issue, i am a building engineer and upon arrival at work today my ACH550 drive was completely off (no power no nothing). i have reached out to our outside contractor but have yet to get a call back. Is there something i can check to see if i can resolve the issue?

  13. #33
    Join Date
    Dec 2012
    Location
    Lowell,MA
    Posts
    69
    Post Likes
    you need to make sure you have power to the drive first, not a lot of " user serviceable " stuff inside, will need ABB guy to look into it

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •