    Hmm ABB ACH550 HVAC speed drive wouldn't turn back on.

    Hello everyone,

    after major renovation speed drives on three floors of high-rise building wouldn't turn on.

    Is there anything that I don't know? Is there a trick on how to start them after long shut-down?

    They have been down for about 2 months and now they are acting as if there was no power to them.
    Screen is completely blank, no sounds of cooling fan, clicking of relays or charging capacitor.
    I have checked all wiring and voltage levels inside and outside the speed drive, and looked through user's manual.
    I thought if you turn the on-off handle on, screen should lit and I should be able to run the motor in hand even if my controls are down.

    Have anyone else stumped on it?

  2. #2
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,398
    Post Likes
    Quote Originally Posted by ddcbacnet View Post
    Hello everyone,

    after major renovation speed drives on three floors of high-rise building wouldn't turn on.

    Is there anything that I don't know? Is there a trick on how to start them after long shut-down?

    They have been down for about 2 months and now they are acting as if there was no power to them.
    Screen is completely blank, no sounds of cooling fan, clicking of relays or charging capacitor.
    I have checked all wiring and voltage levels inside and outside the speed drive, and looked through user's manual.
    I thought if you turn the on-off handle on, screen should lit and I should be able to run the motor in hand even if my controls are down.

    Have anyone else stumped on it?

    Be careful with variable speed drives, think of them like a 600 volt battery that wants to shock the snot out of you.

    It sounds to me like your drives have an integral bypass. If they do, there is a chance they may have a configuration problem.

    My recommendation would be to place a service call with your local ABB rep and have them perform the start up. It would be less expensive than having someone less knowledgeable look at them first and not know how to get them running.

    If the drives need to be re flashed, the ABB rep would be able to do this on the first shot.

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  3. #3
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    If the incoming power to the drive is present and the display stays blank chances are the fuses inside the drive are bad.

  4. #4
    Join Date
    Feb 2013
    Location
    Vancouver, BC
    Posts
    21
    Post Likes
    Thread Starter
    Nope, that's not fuses.
    But I actually like the re flashing idea...
    We have our own ABB certified start-up guy, but he was like wtf?. And he doesn't have a FlashDrop tool.
    Will have to call their office on Monday.

    I'll let you know what happens.

    Thanks!

  5. #5
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,398
    Post Likes
    There should be 24VDC at the terminal strip, if that is not present there is a chance the drive is FUBAR..

    Definitely let us know what transpires.

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  6. #6
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    798
    Post Likes
    Were the VFD's properly shut down before the work was done in the building?

  7. #7
    Join Date
    Jun 2004
    Location
    Olean, NY
    Posts
    1,739
    Post Likes
    In some cases if the drive lacks an external signal at f I think, it can act dead. Comes to life with the enabled command

    Sent from my MZ601 using Tapatalk
    Guinness for strength

  8. #8
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by B_roche View Post
    In some cases if the drive lacks an external signal at f I think, it can act dead. Comes to life with the enabled command

    Sent from my MZ601 using Tapatalk
    I have noticed this also. Freezestat or an emergency shutdown makes everything go out....

  9. #9
    Join Date
    Feb 2013
    Location
    Vancouver, BC
    Posts
    21
    Post Likes
    Thread Starter
    I believe theres no such thing as proper shut down any more. at least not for AHUs. All speed drives now a day come with protection from over- and under-voltages, sudden power loss and shorts and opens on load side.
    Safety interlocks (such as freezestat or FA) are usually normally closed dry contacts that are wired in series with digital inputs and cannot cause power loss of the entire drive.

    We install a few dozens of those things every year, and I can tell you that this case is something much deeper or completely stupid and embarrassing.

  10. #10
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by ddcbacnet View Post
    I believe theres no such thing as proper shut down any more. at least not for AHUs. All speed drives now a day come with protection from over- and under-voltages, sudden power loss and shorts and opens on load side.
    Safety interlocks (such as freezestat or FA) are usually normally closed dry contacts that are wired in series with digital inputs and cannot cause power loss of the entire drive.

    We install a few dozens of those things every year, and I can tell you that this case is something much deeper or completely stupid and embarrassing.
    I won't disagree with you on this. 99% of the time it is wired as you say and says "start enable missing" but you just never know.

  11. #11
    Join Date
    Apr 2012
    Posts
    13
    Post Likes
    I have seen this qiute bit in our system. When power is applied the display remains dark. In the power cabinet the pirmary contactor coil is bad. when you cycle power on this contactor closes to energize the VFD, you said you did not hear anything when power was applied.

  12. #12
    Join Date
    Apr 2012
    Posts
    13
    Post Likes
    An after thought - life safety alarms will have the same affect. Check you smoke and fire safties.

  13. #13
    Join Date
    Feb 2013
    Location
    Virginia
    Posts
    7
    Post Likes
    I would verify correct power to the drive first. If you still dont see anything on the panel I would try changing panels. If you still have no action I would properly lock out power and wait 5 minutes for capcitors to discharge and then check the fuses inside the outside panel. If fuses are good I would call ABB and let them have you check some other things with your meter. BTW someone said previously that your panel would be blank if there is no control signal and thats not true. If there's no signal the panel will still light up but the drive will be in alarm and not work. Hope this helps. gl and be careful!

  14. #14
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    If you remove the panel there is a red and green led I believe , see what they are doing. Then check that 24 VDC power supply.

  15. #15
    Join Date
    Feb 2013
    Location
    Vancouver, BC
    Posts
    21
    Post Likes
    Thread Starter
    yes, there is. they are both off

  16. #16
    Join Date
    Sep 2003
    Location
    Western PA
    Posts
    1,753
    Post Likes
    You may have a bad drive.

  17. #17
    Join Date
    Feb 2013
    Location
    Green Valley AZ
    Posts
    20
    Post Likes
    I'm assuming it's a 480 or 208 primary. If that is present at the drives disconnect, are you making sure it is also getting out to the load side of the disconnect to the drive itself. Sometimes those disconects don't line up well with the handle on the outside of the drive. Those baby's have always lit up if they got power.

  18. #18
    Join Date
    Feb 2013
    Location
    Vancouver, BC
    Posts
    21
    Post Likes
    Thread Starter
    Ok, so...
    Service tech from ABB came over today and declared 3 drives FUBAR on electronic level.

    He took one of the drives with him to run it through some tests and determine the cause.

    Now the cause is obviously somehow related to ongoing construction, but since those drives were wired by previous contractor, my boss ordered to withdraw the drive from the lab, reinstall it in place and let base building deal with it. (Kinda not our wires - not our problem).

    Luckily for me, I have checked the drives before rewiring them. Otherwise would have been my fault.

    :

    Hopefully I will be able to find out what exactly have caused it. Things get pretty interesting...

  19. Likes throrope liked this post.
  20. #19
    Join Date
    Sep 2003
    Location
    Western PA
    Posts
    1,753
    Post Likes
    I doubt you will be able to ever determine the cause of failure. I had the same issue with an ACH550 last summer. Power in and no power out. No LED lights.

  21. #20
    Join Date
    Mar 2012
    Location
    Southern CA
    Posts
    31
    Post Likes
    I know that this particular case has been resolved, but I've also seen a faulty under-voltage relay keep the drive off

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •