    York YK with cold Condenser water

    Check these photo's out, bet your Trane chiller can't do this. First photo is design data, second is flow across evaporator barrel and third is operating data. Under these conditions I have 4650 gpm across the evap, doing approx 1898 tons. The design is 1600 tons. No oil problems everything was running smooth.
    Attached Images Attached Images

  2. #2
    Join Date
    Mar 2012
    Location
    North Carolina
    Posts
    15
    Have you been experimenting with colder condenser water? I have been reading in our YK's engineering manual that you can use an equation to calculate the condenser water temp. According to my calcs we can use condenser water as cold as 40f. I am scared to try it though. When you do that with a YS you'll knock the oil right out of it.

    Our BMS controls the cooling tower bypass. I could put that equation in program and let it determine the condenser water set point. Right now it's fixed at 65 F.

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,530
    YK's are much different than YS's...you can still have tower water that is too cold and it will give you problems, but the YK is much more tolerant than the YS.
    "If you pull one more stunt like you just pulled with Tommy, you won't have to get on a plane because I will personally kick your ass from here to Korea!" - Best of the Best

  4. #4
    Join Date
    Mar 2012
    Location
    North Carolina
    Posts
    15
    Well 40 does seem kind of low but I would like to test out some colder water. But I don't wont to ruin my good chiller because it runs and always has run great

  5. #5
    Join Date
    Jan 2011
    Posts
    1,223
    Quote Originally Posted by chad_nc View Post
    Check these photo's out, bet your Trane chiller can't do this. First photo is design data, second is flow across evaporator barrel and third is operating data. Under these conditions I have 4650 gpm across the evap, doing approx 1898 tons. The design is 1600 tons. No oil problems everything was running smooth.
    4650 GPM when design is 2740?

  6. #6
    Join Date
    Nov 2006
    Location
    North Carolina
    Posts
    130
    Quote Originally Posted by KnewYork View Post
    4650 GPM when design is 2740?
    The max gpm for that evap barrel is around 5400 gpm, I have had them as high as around 4900. I dont want to push it to much. When the machine comes off of the plate heat exchanger over to mechanical cooling the condenser water is in between 47 and 48, It takes a couple of hours to warms the water up to the setpoint of 60 but it runs great. obviously we cant run that much water across the evap in the summer when we have 80 degree condenser water coming back on it.

  7. #7
    Join Date
    Feb 2011
    Location
    OH
    Posts
    149
    have exp on cooler cond water temp it started to surge did not like it went back to flat plate .

  8. #8
    Join Date
    Aug 2009
    Posts
    47
    I have a couple 900 ton CVHF's that take on river water.. Their heat exchanger was down for repair and i had water coming in at 42 haha. No oil loss problems. obviously i had to throttle down on the condenser water to keep it running.
    cvhf.jpg

  9. #9
    Join Date
    Apr 2013
    Location
    NJ
    Posts
    29
    Would running your condenser water temp that low have any effect on your VSD coolant?

  10. #10
    Join Date
    Mar 2007
    Posts
    3,140
    All bets are off when any chiller is operating outside of it's design envelope. This goes for water volume and temperature. Manufacturers shouldn't pitch a customer on the efficiency of their machine based on conditions they may only see a few times a year.

    I know for a fact that you can run Tranes as low as 55 deg F without special accommodations like throttling valves and whatnot. We rarely see condenser water temps that low here, and then only for a few days out of the year.

    I got a question for the OP, can your York run those low condenser water temps without it's liquid level control, variable orifice, and it's associated controls?
    The key to happiness is lower expectations.

  11. #11
    Join Date
    Jan 2011
    Posts
    1,223
    Quote Originally Posted by Tech Rob
    I got a question for the OP, can your York run those low condenser water temps without it's liquid level control, variable orifice, and it's associated controls?
    I'm not the OP, but before the variable orifice came into being the only requirement for the condenser water was it had to be warmer than the leaving chilled water. I've run York YTs with fixed orifice at 50*F without any problem. Remember the variable orifice is there to insure the subcooler remains flooded. The entering condenser water temperature isn't a factor in its operation.

  12. #12
    Join Date
    Nov 2006
    Location
    North Carolina
    Posts
    130
    I got a question for the OP, can your York run those low condenser water temps without it's liquid level control, variable orifice, and it's associated controls? [/QUOTE]


    I am sure it could, with those controls and the cold condenser water it causes the chiller to stack more refrigerant in the condenser which obviously means less in the evaporater. So if the level is set to high under design conditions (which they are not) it could possiblly cause the machine to trip on low evap pressure. Most places around here you dont have the capability to flow that much h2o across the evap, I just thought it would be fun to experiment a little bit. I dont run these machines at those conditions all the time. Also these machines do not have vsd's, they are medium voltage SSS, so I dont have to worry about the starter fluid getting to cold.

  13. #13
    Is this one of the infamous "Chad's" from Greensboro?? Haha

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event