Use of suction line filter-driers?
It is 2013. Sometimes you read about practices from the past and
people mindlessly keep doing what they learned 20 years prior.
I don't want to be such a victim.
After a residential-sized compressor burnout, do people
still ALWAYS install suction-line filter-driers?
Do the acid neutralizer products and modern liquid line filter-drier-"Kleaners"
somehow eliminate that need?
In the past, our shop has been reluctant to install the suction line filters
because of perceived customer objection to the additional cost of removing
the thing a week later. I just want to get a feel for common SUCCESSFUL
practice. Thank you.
Edit: I'm admittedly posting this because I think that installing a suction
line filter aimed at acid cleanup might have saved some repeated visits
recently.Last edited by georgelass; 02-14-2013 at 11:41 PM.
-
02-15-2013, 12:08 AM #2
Professional Member
- Join Date
- Oct 2012
- Location
- Sacramento,ca
- Posts
- 171
After a burn I nitro purge only, install new suction and liquid drier, change both after a few weeks, problem solved. More work, sure, but i think its worth it to not get a call back a year or two later for another bad compressor. I feel the people that are not doing this are setting themselves up to get a nasty call from a customer later
Save yourself some headaches and include the future call to remove filters in your original quote so you are not billing them twice. That always upsets customers. I just explain this is the right way to do it, give them an all inclusive price and i have never had anyone fight me on it.
-
02-15-2013, 07:04 AM #3
Professional Member
- Join Date
- Feb 2013
- Location
- north georiga
- Posts
- 105
i won't replace a compressor with out installing a suction dryer. i also try to get customer to let me spend the extra time to flush the coils, because of plugged cap tubes haunting me in the past. it's a pain but worth it
-
02-17-2013, 11:03 AM #4
Regular Guest
- Join Date
- Feb 2012
- Location
- Moscow
- Posts
- 12
I think the use of suction driers depends on numerous things. If there is a severe comp burn out, rather yes. If in the case of compressor mechanical problem rather no.
-
02-17-2013, 12:02 PM #5
As a matter of best practices I would say that a suction drier should be installed and then removed after the system test clean. But I also think that if you do a acid test before the change out and the system test clean, you could probably get away with nitrogen purge, filter drier, new refrigerant, and a blessing from the dali lama.
"The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
"Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
"Beer is living proof that God loves us and wants us to be happy" --Benjamin Franklin
-
02-17-2013, 12:18 PM #6
-
02-17-2013, 12:43 PM #7
I wouldn't wait a week or more before checking out the pressure drop across the strainer. It may be plugged up by then.
You should check the drop within a couple cays or so and the if it has a drop of 3 or 4 psi above the drop when clean replace it and install another one until you get 2 psi or less increase in your drop after a week or so and then you should remove it and your good to go.
Waited to long to check one once and it had an excessive drop which cause compressor failure. Thank you very much"I could have ended the war in a month. I could have made North Vietnam look like a mud puddle."
"I have little interest in streamlining government or in making it more efficient, for I mean to reduce its size. I do not undertake to promote welfare, for I propose to extend freedom. My aim is not to pass laws, but to repeal them."
Barry Goldwater
-
02-17-2013, 01:22 PM #8
Regular Guest
- Join Date
- Feb 2012
- Location
- Moscow
- Posts
- 12
Sometimes you can't come back to the site in a pair of days. In this case I wouldn't install a strainer. One liquid strainer is enough.
-
02-17-2013, 02:07 PM #9
Professional Member
- Join Date
- Apr 2010
- Posts
- 92
Ugh... haunting memories of installing and then removing suction driers in TRANE resi units. Especially the newer ~16 SEER R410a units. Who can do a handstand while brazing? Good times.
-
02-17-2013, 02:11 PM #10
Professional Member
- Join Date
- Oct 2012
- Location
- Sacramento,ca
- Posts
- 171
-
02-17-2013, 03:52 PM #11
I agree, no point in installing it if the system doesn't need it.
On a more controversial note, while it is best practice to remove the SL filter drier after it has had time to do its job, if there is not a significant pressure drop through it, it isn't hurting anything if it gets left in.
If more government is the answer, then it's a really stupid question.
-
02-17-2013, 10:12 PM #12
Professional Member
- Join Date
- Oct 2012
- Location
- Sacramento,ca
- Posts
- 171
-
02-18-2013, 12:15 AM #13
The subject here is suction line filter driers. Suction line driers will typically have pressure taps on them. LL driers typically won't.
As for your initial comment, there won't be a temperature drop across either a suction line drier or liquid line drier unless there is at least some liquid going into it, and a liquid/vapor mixture going out of it. If you have either gas-in-and-gas-out or liquid-in-and-liquid-out, then you get no temperature drop. In either of these two cases you'd typically need some means of measuring the pressure drop directly. Adding a pressure tap is the only practical way to do that in some cases, so don't hesitate to do that when you suspect a restriction and aren't seeing a temperature drop.
You can have a significant restriction with no temperature drop across it so don't assume that there's no restriction just because there's no temperature drop. IOW, what you've always been told is wrong at face value. There's a lot more to be said, but you can search the forum for threads that cover this topic.


Reply With Quote