York Chiller VSD 503 "Motor Controller Loss of Current"
The entire power assembly was replaced on this chiller VSD as well as the vyper logic board. The run light on the vyper board shows up but no lights on the individual driver boards. Its like its commanded to run but not running, eventually the drive trips out of loss of current because it's obviously pulling no current.
Anybody have any suggestions?
ThanksIMG_0614.jpg
-
02-14-2013, 06:35 PM #2
why was it replaced? sounds like a wiring issue to me....from here....on Mars....i mean, uh, Earth...yeah, Earth.
The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?
-
02-16-2013, 11:18 PM #3
Professional Member*
- Join Date
- Dec 2008
- Location
- Dixiana, AL
- Posts
- 2,487
Why - and by whom - was it replaced? You're not giving much info to try and formulate an answer from, but I'll tell you what jumps out at me - a vyper drive only has one driver board on one output pole. You indicate that you have multiple gate drivers. You might want to start looking there.
-
02-17-2013, 06:43 AM #4
“MOTOR CONTROLLER – LOSS OF
CURRENT”
The Compressor Motor current decreased to 10% Full
Load Amps (FLA) for 25 continuous seconds while the
chiller was running. This could be caused by the starter
de-energizing during run or a defect in the motor current
feedback circuitry to the Control Center. The chiller
will automatically restart at the completion of “System
Coastdown”.Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.


Reply With Quote