    York Chiller VSD 503 "Motor Controller Loss of Current"

    The entire power assembly was replaced on this chiller VSD as well as the vyper logic board. The run light on the vyper board shows up but no lights on the individual driver boards. Its like its commanded to run but not running, eventually the drive trips out of loss of current because it's obviously pulling no current.

    Anybody have any suggestions?

    ThanksIMG_0614.jpg

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,879
    Post Likes
    why was it replaced? sounds like a wiring issue to me....from here....on Mars....i mean, uh, Earth...yeah, Earth.
    How to lose weight fast...under-cooked chicken.

  3. #3
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,619
    Post Likes
    Why - and by whom - was it replaced? You're not giving much info to try and formulate an answer from, but I'll tell you what jumps out at me - a vyper drive only has one driver board on one output pole. You indicate that you have multiple gate drivers. You might want to start looking there.

  4. #4
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,642
    Post Likes
    “MOTOR CONTROLLER – LOSS OF
    CURRENT”
    The Compressor Motor current decreased to 10% Full
    Load Amps (FLA) for 25 continuous seconds while the
    chiller was running. This could be caused by the starter
    de-energizing during run or a defect in the motor current
    feedback circuitry to the Control Center. The chiller
    will automatically restart at the completion of “System
    Coastdown”.
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Quality Home Comfort Awards