I was able to add a device manually and commission it through workbench. The device came online in the nae but niw I cant add points. Im looking for the mcquay whpe3b xif file. If I add that to the nae will I be able to discover the points?
-
02-14-2013, 02:05 PM #2
Professional Member
- Join Date
- Oct 2009
- Posts
- 490
Whpe3b is the number on the echelon board, but when I bring it in through niagara module://lonMicrotech/Whpe1B.lnml is used as the XML file. Is there a way to convert this back to an XIF or extract the lnml out of workbench?
-
02-15-2013, 02:52 PM #3
Professional Member
- Join Date
- Oct 2009
- Posts
- 490
Ok I was able to find the right file and add it as a resource file to the nae. After I did a reboot to the nae it was able to discover the points in the heatpump.