    Thanks for everyone's input. Chalk this up to a lesson learned.

  2. #15
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,143
    Post Likes
    GCPM, if I were you I would try contacting McQuay about any possible warranty coverage. The OEM's are all familar with "special" circumstances concerning startups. Delays are not that unusual. There may be "wiggle" room in the warranty period. Even if there isn't, I've seen concessions given to keep a customer happy.

  3. #16
    Join Date
    Aug 2009
    Location
    Ontario, Canada
    Posts
    64
    Post Likes
    Any Tech with experience on the turbocor can pull the fault logs off of the compressor to check what happened and the last time it ran. If the fault logs are pulled and the Tech on site is still questioning why the compressor failed then the fault logs can be sent to Danfoss/Turbocor and there tech support can check the fault logs and they will give you the cut and dry truth of why the compressor failed.
    I have found in the past before I was factory trained at Danfoss/Turbocor the the Mcquay tech and there tech support are not very knowledable with there WMC machines but there are a few exception out there

    Good Luck

  4. #17
    Join Date
    Jun 2009
    Location
    San Diego, CA
    Posts
    21
    Post Likes
    Standard warranty from Danfoss Turbocor is 12 months from start up or 18 months from date of shipment.

    However, we as the OEM's can extend the warranty however we see fit, based upon if an extended warranty was bought, etc.

    McQuay buys a lot of compressors at a time and are usually one revision behind current production at DTC. So if DTC is building revision "E" they still might be using revision "D". This was done strategically by McQuay because for so long every time you would get a new compressor revision from DTC, you would have to modify controls to accommodate the new revision. A perfect example of this was the transition from Milestone 1 to Milestone 2 in BMCC software