Thread: Johnson-FXVMA-RemoteDisplay MUI Software Emulation

  1. #1
    Join Date
    Feb 2013
    Location
    Montreal, QC, Canada
    Posts
    2
    Post Likes

    Johnson-FXVMA-RemoteDisplay MUI Software Emulation

    Good day gentlemen,
    I need a remote display to correct a flaw in the FXVMA where the engeneering units go back to US after a power down. FSC says the solution is to temporarily connect a remote MUI set the units to SI and remove the MUI. This needs to be done once only.

    I would prefer a windows based software emulator to the MUI rather than the extra expense for one time use.

    Has anyone got that type of program?

    Many thanks for taking the time to read this!

    Maurice

  2. #2
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    730
    Post Likes
    Add an MUI to the FXVMA configuration. Add UoM, set to SI, to the MUI. Save. Download. No need for the physical device.
    UA LU 562

  3. #3
    Join Date
    Feb 2013
    Location
    Montreal, QC, Canada
    Posts
    2
    Post Likes
    Thread Starter
    I'm afraid I have already done what you propose and this seemed to work in the past. In this instance after a download it does show values to the FX60 as SI (specifically °C) but after a power down of the FXVMA it returns to US (specifically °F) . The values follow the engeneering unit so that zone temperature may show 20°C after a download of its apd and after a power loss it will show 68°C.
    The Johnson paper does specify using an MUI after startup.

    Many thanks for your help

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •