Thread: Station Starting
-
02-13-2013, 03:09 PM #1
Station Starting
I have a new account with 49 BacNet Spyders on a 600. We proposed splitting the network up to help with some communication issues.
So I installed the new com card and redid wiring. When I started the Jace back up I noticed it was taking a while to start the station.
I'm get in the director- "[honeywellSpyderTool] Station startup sequence returning" over and over again, then finally the station starts. I counted that it does it the same number of times as devices I have on the network.
Any ideas what it means? Never seen this message before.
Btw- This is a Vykon Jace 3.5.34 with SpyderTool 4.8.8
-
02-13-2013, 04:30 PM #2
Professional Member
- Join Date
- Feb 2013
- Location
- Phoenix, AZ
- Posts
- 194
It was doing the same thing before you split the comms, it always does a startup line for each device. I've seen the same thing whether LON, or BACnet controllers.
Sent from my ADR6300 using Tapatalk 2
-
02-13-2013, 04:46 PM #3
-
02-13-2013, 04:55 PM #4
To be honest, I don't know if it did it before I split the network. Never rebooted the station. Only my second time there.
The initializing makes sense, since there is no engineering mode.
Most of my Spyder experience has been with AX 3.6 and Spydertool 5.2.
I'm just glad there is nothing wrong. I couldn't even imagine if the network was big, what the station start up time would be.