Thread: Johnson Metasys/CCT state tables
-
02-23-2013, 07:38 PM #14
Regular Guest
- Join Date
- Feb 2013
- Posts
- 9
A little off topic, since it seems you are well into the Johnson products...can anybody answer this, I just downloaded a new FX-PCT programming and commissioning tool from Johnson controls. The very first page top left has the 'configure' and 'commission' tabs and the top right has the 'select system' and 'define hardware' tabs, for some reason the 'commission' tab is the only one that allows access in the program and commission only. I'm trying to configure a new controller and the 'configure', 'select system' and 'define hardware' tabs don't allow access.
Anybody have the same problem with this?
-
02-23-2013, 09:45 PM #15
Professional Member
- Join Date
- Nov 2005
- Location
- Shreveport, Louisiana
- Posts
- 2,240
Commisioning only version usually given to TAB people to do there part of the job.
UA Local 141
-
03-06-2013, 08:52 AM #16
We did get an answer to our email, and all of the above is exactly correct. The State table was not used. He used a couple of 'Command Hierarchy's here and there. So, as long as we don't try to view it, or print a report, it does not blow up, and we expect it to work.
Thanks for the research, and sorry it took me so long to respond - I missed your post somehow.
Jim A.