    Lon add device error
    I was trying to add a mcquay heatpump to my lon network. I was able to discover it but when it tried to add it into the database I got the error "Duplicate Tag: Whpe2e=1". This is the only device that was on the network. I got it to work by adding it from the palette and using match. I added a screenshot, just curious why this wouldnt let me add it by the discover method. I am also new to lon, so its probably something simple.
    Jan 2005
    When doing an add from a discover the device will default to a subnet of 1 with a node of 1 in the window that pops up after you click to add the device. This usually matches the subnet and node of the first device you added. Change the node to another number not assigned to any other device. I usually like to put them in the order that I add them, second device would be node 2 the third device would be 3 and so on.
    Build it and it will break. Fix it and it will work. Ignore it and will cost more. Patch it and it will get worse. Cross the bridge before the flood.
    Oct 2005
    Southern California
    I had the same problem when I added certain Circon controllers. Circon has two jar files for their devices. The controllers were listed under both jars.