Thread: Lennox RTU, manifold pressure

  1. #1
    Join Date
    Feb 2013
    Location
    Tri-Cities, Ontario
    Posts
    8
    Post Likes

    Lennox RTU, manifold pressure

    Working on a GCS16-653-125-3J. Im not to familiar with these units. My issue is my manifold pressure jumps up and down. From a high of 2.8" to just below 1". I have a rock steady inlet pressure of 6.6"
    Any help would be great.
    Thanks

  2. #2
    Join Date
    Feb 2012
    Location
    Ottawa, Ontario Canada
    Posts
    40
    Post Likes
    Gas valve.... dont think those rtu's have slow opening gas valves but could have crap in the gas valve. I'd replace.

  3. #3
    Join Date
    Feb 2013
    Location
    Tri-Cities, Ontario
    Posts
    8
    Post Likes
    Thread Starter
    This is the 2nd valve, original valve did the same thing.

  4. #4
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    I believe 2.8" lowfire and 3.7" wc highfire is what you should have
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  5. #5
    Join Date
    Feb 2013
    Posts
    3
    Post Likes
    Two stage valve?

  6. #6
    Join Date
    Feb 2013
    Location
    Tri-Cities, Ontario
    Posts
    8
    Post Likes
    Thread Starter
    Its single stage, Manufactures specs call for 2.7".

  7. #7
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Sounds like you may have a manometer issue. Cracked hose?

  8. #8
    Join Date
    Feb 2013
    Posts
    3
    Post Likes
    Is that model one with the " gun type" burner, where the inducer mounts with the gas line and blows the flame into the heat exchanger?

  9. #9
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    A little off topic but I hate gcs units.

    Sent from my SGH-T999 using Tapatalk 2

  10. #10
    Join Date
    Feb 2013
    Location
    Tri-Cities, Ontario
    Posts
    8
    Post Likes
    Thread Starter
    manometer is six months old and my hoses are fine. The same hose and meter was used to test all my other pressures at the same time.
    The burner is kind like an in-shot, the heat exchanger is kind of diamond shape to tubular to combustion fan. If that makes sense?

  11. #11
    Join Date
    Sep 2008
    Location
    rensselaer,ny
    Posts
    120
    Post Likes
    what kind of issue you having with unit , I had one giving me problems it was heat exchanger ,new exchanger replaces the one inshot burner design.

  12. #12
    Join Date
    Feb 2013
    Location
    Tri-Cities, Ontario
    Posts
    8
    Post Likes
    Thread Starter
    I'm getting low temp rise, 15 - 20 deg F. Manufactures specs 40 - 70 deg F. Indoor fan speed is ok, im not getting any outside air in, and i tried to clock the meter, i couldn't tell the scale of the dail due to the age of the meter. My guess is that im only burning 61000 btuh. Units input is 125000.

  13. #13
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    And the inlet stays at 6.6" the entire time?

    Sent from my SGH-T999 using Tapatalk 2

  14. #14
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,420
    Post Likes
    either another bad valve ...or something restricting the gas flow..... inlet pressure fine ...outlet low..... usually the valve......
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  15. #15
    Join Date
    Feb 2013
    Location
    Tri-Cities, Ontario
    Posts
    8
    Post Likes
    Thread Starter
    yup, inlet stays at 6.6" the whole time

  16. #16
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Is there a regulator in the line that could be acting up?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  17. #17
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Is this the customers only unit?

    Anything else on their meter?

  18. #18
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    263
    Post Likes
    does voltage to the valve stay constant

  19. #19
    Join Date
    Feb 2013
    Location
    Tri-Cities, Ontario
    Posts
    8
    Post Likes
    Thread Starter
    Only unit on that meter, no regulator up stream, voltage stay constant.
    Talked to Lennox tech support and after a lot of talking, he thinks i have an inducer issue.
    I'm heading back there tomorrow morning, i'll post any updates.

  20. #20
    Join Date
    May 2000
    Location
    Salem, WI US
    Posts
    83
    Post Likes
    I would check the burner orifice for an obstruction, if the manifold pressure is fluctuating this much there has to be some sort of blockage in the burner. I am assuming you replaced the gas valve.

    Beta

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •