Results 14 to 23 of 23
Thread: Lennox RTU, manifold pressure
-
02-12-2013, 11:43 PM #14
either another bad valve ...or something restricting the gas flow..... inlet pressure fine ...outlet low..... usually the valve......
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
02-13-2013, 07:02 AM #15
Regular Guest
- Join Date
- Feb 2013
- Location
- Tri-Cities, Ontario
- Posts
- 8
yup, inlet stays at 6.6" the whole time
-
02-13-2013, 10:07 AM #16
Is there a regulator in the line that could be acting up?
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
02-13-2013, 03:17 PM #17
Is this the customers only unit?
Anything else on their meter?
-
02-13-2013, 03:30 PM #18
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 167
does voltage to the valve stay constant
-
02-13-2013, 05:27 PM #19
Regular Guest
- Join Date
- Feb 2013
- Location
- Tri-Cities, Ontario
- Posts
- 8
Only unit on that meter, no regulator up stream, voltage stay constant.
Talked to Lennox tech support and after a lot of talking, he thinks i have an inducer issue.
I'm heading back there tomorrow morning, i'll post any updates.
-
02-13-2013, 07:47 PM #20
Professional Member
- Join Date
- May 2000
- Location
- Salem, WI US
- Posts
- 42
I would check the burner orifice for an obstruction, if the manifold pressure is fluctuating this much there has to be some sort of blockage in the burner. I am assuming you replaced the gas valve.
Beta
-
02-14-2013, 06:49 AM #21[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
02-14-2013, 05:20 PM #22
Regular Guest
- Join Date
- Feb 2013
- Location
- Tri-Cities, Ontario
- Posts
- 8
-
02-15-2013, 02:41 PM #23
Normally, when you have a partially blocked orifice, the flame will appear different than the other burner flames. Do you recall seeing any difference in the flame?


Reply With Quote