Page 2 of 2 FirstFirst 12
Results 14 to 23 of 23
  1. #14
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,416
    Post Likes
    either another bad valve ...or something restricting the gas flow..... inlet pressure fine ...outlet low..... usually the valve......
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  2. #15
    Join Date
    Feb 2013
    Location
    Tri-Cities, Ontario
    Posts
    8
    Post Likes
    Thread Starter
    yup, inlet stays at 6.6" the whole time

  3. #16
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    5,991
    Post Likes
    Is there a regulator in the line that could be acting up?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  4. #17
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    29,259
    Post Likes
    Is this the customers only unit?

    Anything else on their meter?

  5. #18
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    261
    Post Likes
    does voltage to the valve stay constant

  6. #19
    Join Date
    Feb 2013
    Location
    Tri-Cities, Ontario
    Posts
    8
    Post Likes
    Thread Starter
    Only unit on that meter, no regulator up stream, voltage stay constant.
    Talked to Lennox tech support and after a lot of talking, he thinks i have an inducer issue.
    I'm heading back there tomorrow morning, i'll post any updates.

  7. #20
    Join Date
    May 2000
    Location
    Salem, WI US
    Posts
    83
    Post Likes
    I would check the burner orifice for an obstruction, if the manifold pressure is fluctuating this much there has to be some sort of blockage in the burner. I am assuming you replaced the gas valve.

    Beta

  8. #21
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    29,259
    Post Likes
    Quote Originally Posted by Slim_Miller View Post
    Only unit on that meter, no regulator up stream, voltage stay constant.
    Talked to Lennox tech support and after a lot of talking, he thinks i have an inducer issue.
    I'm heading back there tomorrow morning, i'll post any updates.
    And you are certain that there is a steady pressure coming to the unit from the meter, right?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  9. #22
    Join Date
    Feb 2013
    Location
    Tri-Cities, Ontario
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by Betabass View Post
    I would check the burner orifice for an obstruction, if the manifold pressure is fluctuating this much there has to be some sort of blockage in the burner. I am assuming you replaced the gas valve.

    Beta
    You nailed it.
    Orifice was partly blocked. It was burning fine but was making my vacuum in the burner box fluctuate, making my manifold pressure go crazy. Everything is great now.
    Thanks everyone for your ideas

  10. #23
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    29,259
    Post Likes
    Normally, when you have a partially blocked orifice, the flame will appear different than the other burner flames. Do you recall seeing any difference in the flame?

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.