Results 14 to 23 of 23
    Apr 2012
    winnipeg
    either another bad valve ...or something restricting the gas flow..... inlet pressure fine ...outlet low..... usually the valve......
    Feb 2013
    Tri-Cities, Ontario
    yup, inlet stays at 6.6" the whole time
    Oct 2011
    Chicagoland Area
    Is there a regulator in the line that could be acting up?
    Southeastern Pa
    Is this the customers only unit?
    Anything else on their meter?
    willowick ,oh
    does voltage to the valve stay constant
    Feb 2013
    Tri-Cities, Ontario
    Only unit on that meter, no regulator up stream, voltage stay constant.
    Talked to Lennox tech support and after a lot of talking, he thinks i have an inducer issue.
    I'm heading back there tomorrow morning, i'll post any updates.
    Salem, WI US
    I would check the burner orifice for an obstruction, if the manifold pressure is fluctuating this much there has to be some sort of blockage in the burner. I am assuming you replaced the gas valve.
    Beta
    Southeastern Pa
    Quote Originally Posted by Slim_Miller View Post
    And you are certain that there is a steady pressure coming to the unit from the meter, right?
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Feb 2013
    Tri-Cities, Ontario
    Quote Originally Posted by Betabass View Post
    Beta
    You nailed it.
    Orifice was partly blocked. It was burning fine but was making my vacuum in the burner box fluctuate, making my manifold pressure go crazy. Everything is great now.
    Thanks everyone for your ideas
    Southeastern Pa
    Normally, when you have a partially blocked orifice, the flame will appear different than the other burner flames. Do you recall seeing any difference in the flame?