Results 1 to 13 of 13
Thread: wind roll out issues
-
02-12-2013, 04:50 PM #1
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
wind roll out issues
carrier 48aje has a chronic roll out tripping problem, over the years many solution were tried and still doing it every time the wind blows hard, carrier tech support ran out of ideas, besides replacing the unit what else is there to do?
-
02-12-2013, 06:14 PM #2
Regular Guest
- Join Date
- Feb 2013
- Location
- Michigan
- Posts
- 6
Im Just curious if you have looked at the heat exchanger? A lot of times I have found them cracked.
-
02-12-2013, 07:02 PM #3
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
-
02-12-2013, 07:09 PM #4
-
02-12-2013, 07:13 PM #5
Just a shot in dark, is the inducer cutting out at all? I had a carrier 10 ton with a bad inducer that would roll out. It would not shut down all the way though to affect the Hall effect switch.
Sent from my iPad using Tapatalk HDTo the man who always did it right. I love you dad and I will miss you to much for words.
Stay Thirsty My Friends
Support the Skilled Trades Don't DIY
-
02-12-2013, 08:11 PM #6
Regular Guest
- Join Date
- Feb 2013
- Location
- Michigan
- Posts
- 6
Yeah if it a horizontal discharge it is hard if is a downflow pull of that plate on the end and look at the seems on the heat hanger tubes a lot of times they will be rotten out not so much cracked. And it happens where they join the metal together the whole length of the tube. If I remember correctly it should be about 10 or 11 o'clock if you are looking at it from the access panel end.
-
02-12-2013, 08:26 PM #7
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
The inducer runs ok, the unit runs for weeks without tripping then on a windy day we get the call, it has two 300K btu's burners assemblies twined, the burner closer to the condenser coil trips most of the time.
-
02-12-2013, 08:47 PM #8
Well you know you have a cracked heat exchanger. Guess that would be the place to start. Do you know how long it has been like that? Just wondering if it was cracked when the first call came in.
Sent from my iPad using Tapatalk HDTo the man who always did it right. I love you dad and I will miss you to much for words.
Stay Thirsty My Friends
Support the Skilled Trades Don't DIY
-
02-18-2013, 06:38 PM #9
Regular Guest
- Join Date
- Aug 2012
- Posts
- 6
your cracked heat exchanger is definitley the culprit, it causes the slower velocity of the combustion fumes and the flames have a harder time pulling thru properly, hence on a windy day they dont suck in to well
-
02-18-2013, 10:27 PM #10
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
-
02-18-2013, 10:30 PM #11
So these flue pipe add ons I see aren't a recommended thing huh?
Sent from my SGH-T999 using Tapatalk 2
-
02-18-2013, 10:51 PM #12
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
-
02-18-2013, 11:14 PM #13


Reply With Quote