Results 1 to 2 of 2
Thread: FX Jace content filter
-
02-12-2013, 04:16 PM #1
Professional Member
- Join Date
- Oct 2009
- Posts
- 490
FX Jace content filter
Does anyone know how to go from UI+Runtime to just Runtime in an FX Jace? I went through and selected the option through the commissioning wizard but there was no change in the modules. I followed the steps in the workbench users guide also, but that didnt work either. Are there specific modules that need to be reinstalled? Here is what the workbench users guide says:
If you restrict the content level (go from ui+runtime to runtime), modules
already installed are not automatically reinstalled (to reduce storage). You need
to click Finish, and platform/station operation is otherwise unaffected;
however, if you later reinstall existing modules, or install new modules, the
new content filter level is applied, typically with resulting savings in storage
space. Therefore, if freeing storage space is the goal when restricting module
content, after changing the content level, you should reinstall existing modules.
Do this action using the Software Manager.
-
02-12-2013, 05:39 PM #2
Sounds like you just need to reinstall all of the existing modules for the filter to apply. You can do that from the software manager view. Highlight all of the "Up to Date" modules and click Re-install.


Reply With Quote