Page 2 of 2 FirstFirst 12
Results 14 to 16 of 16
  1. #14
    Join Date
    Aug 2012
    Posts
    1,520
    You guys are awesome.
    Certified parts changer.

  2. #15
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,154
    Quote Originally Posted by timebuilder View Post
    AND the unit must have the correct power distribution parts, as shown above, AND the unit disconnect MUST be within sight of the unit. This is NOT the breakers in the unit.
    Actually, if the unit has integral breakers, like the air handler I pictured, they count as the means of disconnect, so you don't need another disconnect within sight.
    If more government is the answer, then it's a really stupid question.

  3. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    14,482
    Quote Originally Posted by mark beiser View Post
    Actually, if the unit has integral breakers, like the air handler I pictured, they count as the means of disconnect, so you don't need another disconnect within sight.

    You are correct. The stipulation in 422.19 (A) is intended to cover fuses used as supplementary overcurrent protection. I used to see a lot of units with fuses. My bad.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •