    You guys are awesome.
    It's not if your doing it right it's whether your doing the right thing that is important.

  2. #15
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes
    Quote Originally Posted by timebuilder View Post
    AND the unit must have the correct power distribution parts, as shown above, AND the unit disconnect MUST be within sight of the unit. This is NOT the breakers in the unit.
    Actually, if the unit has integral breakers, like the air handler I pictured, they count as the means of disconnect, so you don't need another disconnect within sight.

  3. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    28,227
    Post Likes
    Quote Originally Posted by mark beiser View Post
    Actually, if the unit has integral breakers, like the air handler I pictured, they count as the means of disconnect, so you don't need another disconnect within sight.

    You are correct. The stipulation in 422.19 (A) is intended to cover fuses used as supplementary overcurrent protection. I used to see a lot of units with fuses. My bad.