standing wall heater, milivolt/microamp volt readings?
ok so i dont work on a lot of these but on a service call for no heat,
The pilot lights and stays lit, it puts out voltage to gas valve at around 105Ua, checked the t-stat and it works and i jumped it out just in case and no gas will come out of valve and I also cleaned the the thermocouple and checked all limits.. all seem to be working yet no gas coming from valve.
So two questions how many micro amps/volts does it take to open the valve and what is the reading supposed to be coming from a flame generated sensor?
Im pretty sure its the gas valve but just double checking..thanks
-
02-11-2013, 06:28 PM #2
Professional Member*
- Join Date
- Jul 2010
- Location
- nebraska
- Posts
- 1,167
Good thermocouple should put out around 25 millivolts,no lower than 20. Meter can't be set on microamps to check thermocouples.
-
02-11-2013, 06:53 PM #3
are you talking about a thermocouple or a thermopile? above post is good for thermocouple but thermopile is around 750 millivolts. You can tell it is a thermopile as it will be larger than a thermocouple.
dogboy
-
02-12-2013, 11:01 AM #4
Professional Member
- Join Date
- Nov 2008
- Location
- DFW,TX
- Posts
- 1,891
i guess its a thermopile because IT GENERATES THE MILLIVOLTS needed to power the tstat and gas valve on a wall heater.. how do you measure that to make sure its enough.. i had 105 microamps so it was putting out volts so where do i take the reading and whats the normal range?
-
02-12-2013, 11:27 AM #5
AS stated above generally they put out 750 millivolts. there may be different outputs but the ones I used were 750mv. You got 105 millivolts. So I guess you check it the way you did, with the meter across the thermopile. Microamps has nothing to do with it.
look at the second page.
http://www.robertshawtstats.com/spaw...oltSystems.pdf
dogboy
-
02-12-2013, 01:04 PM #6
Professional Member
- Join Date
- Nov 2008
- Location
- DFW,TX
- Posts
- 1,891
good link, thanks man..
BTW im not sure i was using my meter correctly but i was checking with my FP SC 56 meter with the dial select on the uA setting and that where i measure the 105 at across the first two terminals on the block while flame pilot was lit.. what setting on my meter do i use to measure milivolts ?
-
02-12-2013, 01:19 PM #7
Professional Member*
- Join Date
- Oct 2011
- Location
- Las Vegas, NV
- Posts
- 346
-
02-12-2013, 01:20 PM #8
I would say vdc as your meter should auto range down to millivolts. Are you a technician? as this is pretty basic.
dogboy
-
02-12-2013, 01:37 PM #9
Professional Member
- Join Date
- Nov 2008
- Location
- DFW,TX
- Posts
- 1,891
yes and a damn good one but sometimes i run across crap like this that i dont see very often and want to make sure i am doing things correctly.. we are 80% cooling and 20% heating here in DFW,TX and i dont see many Millivolt systems(maybe 6 in 15 yrs) and we typically replace them not repair them so i wanted to brush up on this info..
-
02-12-2013, 04:06 PM #10
Professional Member*
- Join Date
- Apr 2001
- Location
- MINN
- Posts
- 932
-
02-12-2013, 04:08 PM #11
If it is a White Rogers thermopile throw it away and get a Honeywell. I've had so many bad White Rogers t'stats and other parts that I refuse to buy them any more.
-
02-12-2013, 07:42 PM #12
-
02-12-2013, 07:44 PM #13
another double post.