+ Reply to Thread
Results 1 to 7 of 7

Thread: Duravent poly pro venting

  1. #1
    Join Date
    Aug 2011
    Location
    Fort Mcmurray,Ab
    Posts
    55
    Post Likes

    Duravent poly pro venting

    Has anyone used the poly pro venting system from Duravent? It says you can vent two appliances thru 1 pipe like b-vent but its 636 rated.

  2. #2
    Join Date
    Dec 2011
    Location
    somewhere between here and there
    Posts
    478
    Post Likes
    was just at a seminar...... dont remember the guy saying that could vent 2 apliances tho......


    Please, Please Please......keep the Factory Smoke in the Wires!!!!!


    Is it Rum'Oclock yet???

  3. #3
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    That's sounds like a bad idea....

  4. #4
    Join Date
    Aug 2011
    Location
    Fort Mcmurray,Ab
    Posts
    55
    Post Likes
    Thread Starter
    Their website shows examples of multi units being vented and it looks interesting

  5. #5
    Join Date
    Nov 2011
    Location
    Long Island, NY
    Posts
    352
    Post Likes
    I don't know about venting more than one appliance, but we use it all the time. Just make sure it is supported well on horizontal runs otherwise it will sag and we all know that's not good with condensing equipment. It is even easier to use than PVC.

  6. #6
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes
    It is not approved for CAT I as B-vent and chimneys are. It shows using it to reline B-vent, which is highly controversial since it was not listed this way. Time will tell. It is listed for CAT II and IV but not III so be careful of your applications.

    Anything that vents under positive pressure cannot be common vented with other appliances regardless of what a vent mfr. says. I will talk with Dale Menges in Tech Svcs. this week about this.

  7. #7
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by hearthman View Post
    It is not approved for CAT I as B-vent and chimneys are. It shows using it to reline B-vent, which is highly controversial since it was not listed this way. Time will tell. It is listed for CAT II and IV but not III so be careful of your applications.

    Anything that vents under positive pressure cannot be common vented with other appliances regardless of what a vent mfr. says. I will talk with Dale Menges in Tech Svcs. this week about this.
    I actually talked with regional sales about that issue.

    Polypro CAN be used for common venting, IF the manufacturer of the appliances allows common venting (commonly known as cascading).

    If the appliances you are venting are not approved by the manufacturer for cascading, then you cannot use polypro for cascading.
    If the appliance is not approved by the manufacturer for polypro at all, then you cannot use polypro.

    This has to do with the liability and certifying. They are approving their pipe for it's usage in general, not for it's usage to specific applications.


    hearth can maybe explain it in more technical terms, but basically:

    Follow manufacturers recommendations.
    If you want to use polypro for a specific appliance, then you need to look at polypro's certification sheet:
    http://www.duravent.com/docs/product...oApprovals.pdf
    There is nothing special about polypro that allows you to do anything different than you would with regular PVC, baring the (vertical only) flexible chase (which is clearly still not seen the end of approvals),


    We looked into this as solution for removing 80% water heater/furnaces in stacked condos, and replacing with all 90% equitment if the law were to require it.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •