    Automatic vent damper for Weil-McLain boiler?

    My house currently has a Weil-McLain boiler, model CGM-6-PI. It has an automatic vent damper that was installed in 1991, but that is sticking in the closed position (I can get it to open by giving it a little jiggle or tap, but it's not a sustainable situation). Think I need to replace the automatic vent damper, but am trying to figure our what models are compatible. If anyone has any suggestions and information, I would appreciate it. Also, can this be a DIY job for someone moderately handy? Though I generally don't mess at all where gas and the boiler are involved, provided I have the right part and wiring harness, this doesn't look like it ought to be overly difficult.

    Thanks in advance.

  2. #2
    Join Date
    Aug 2003
    Location
    Central Kentucky
    Posts
    6,247
    Chuck the automatic vent damper & get a contractor trained in CO/Combustion diagnostics to install a barometric damper.

    It will work better & be much safer than the automatic type.

    Check out www.nationalcomfortinstitute.com for contractors in your area that have been through CO training.
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,758
    Quote Originally Posted by davidr View Post
    Chuck the automatic vent damper & get a contractor trained in CO/Combustion diagnostics to install a barometric damper.

    It will work better & be much safer than the automatic type.

    Check out www.nationalcomfortinstitute.com for contractors in your area that have been through CO training.


    Why not a barometric in conjuntion with an automatic.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    17,827
    How bout an automatic barometric damper?
    "Politicians are the lowest form of life on Earth. Liberal Democrats are the lowest form of politician"

    - General George S. Patton

  5. #5
    Join Date
    Aug 2003
    Location
    Central Kentucky
    Posts
    6,247
    Quote Originally Posted by beenthere View Post
    Why not a barometric in conjuntion with an automatic.

    Would not think it would be needed as the pressure drop of the heat exchanger would have to be accounted for with the addition of a barometric.

    Might run the possibility of nuisance tripping a spill switch if it is equipped with an automatic damper as well.

    Barometrics I trust, automatic type dampers I don't.
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event