    Commercial Ruud Water Heater eats thermocouples

    almost like clock work , every 4 months the pilot will not light , replace TC , good to go another 4 months

    Replaced gas valve 3 years ago , same problem

    What in the world could it be ? I use the standard Honeywell TC 36" you find anywhere

    Pilot flame looks nice .... keeps it cherry red
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	2013020995212707.jpg 
Views:	106 
Size:	49.0 KB 
ID:	355941   Click image for larger version. 

Name:	2013020995212731_2.jpg 
Views:	60 
Size:	35.8 KB 
ID:	355951  

  2. #2
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    5,368

    Question

    What's your inlet pressure? What's up with that nasty room? Do you have adequate makeup air and no source of depressurization? What about the rest of the venting? Have you tested at the floor with a combustion analyzer to ensure its not suffocating by CO2 displacing the O2?

  3. #3
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,172
    Next time your at the parts house check on the Husky thermocouples. I haven't had any issues with thermocouples sense I switched brands. There about three times the cost but well worth the money.
    Do NOT click HERE

  4. #4
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,092
    Quote Originally Posted by Snapperhead View Post
    Pilot flame looks nice .... keeps it cherry red
    If it is keeping it cherry red, that may be a big part of the problem. Over heating a thermocouple can DRASTICALLY reduce its life, and "cherry red" is way to hot.
    The pilot flame should also only be hitting the last 1/2 inch or so of the thermocouple. If the flame is hitting much lower than that, it can make less voltage, and shorten its life.
    If more government is the answer, then it's a really stupid question.

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    2,184
    Outlet was 3.7 , didnt check inlet , dont have combustion analyzer , venting on its own flue out the roof

    Nasty room is a utility room in a pizza joint beside 2 walk-ins , entrance is always open

    That makes sense about the glowing cherry red being a problem. Its hitting halfway down the rod. Thats probly my issue.

    Any other appliance I've seen its hitting the tip.

    Hmmmmmmm

    Im going back and make an adjustment !