Results 14 to 25 of 25
    Dec 2011
    New Zealand
    All ways an interesting one.
    As stated above a sight glass is a tool and used as an aid to charging, generally speaking your pure refrigerants, are normally better than mixtures using a sightglass method. (with mixtures very small pressure drops, valves, driers etc. can cause bubbles) At times of very high load, it sometimes difficult to get a full sightglass when the valve is 100% open especially the TXV is slightly on the larger size of the required duty.
    Superheat is also a good method, but normally only when your room or product (one pass chillers) is close to set point.
    So it more down to understand at what stage your system is at and what condensing control you have. (also stated above)
    The only time you cant use a sight glass is when you have a headmaster , because even after the sight is cleared you still need to add a little more , and there is a procedure for measuring that amount.
    This one never goes away.......it depends on what type of system you are working on. The answer to this question is always yes. However, it depends on what type of system you are working on. The debate rages on that if you have a full column of liquid in the liquid line you should have a clear sightglass. On cap tube systems, due to may reasons, the sightglass may always flash and never clear. There is a better reason to use a sightglass on systems. And that is for moisture reasons. I have my guys install sightglasses on all refrigeration systems for this very reason. On top of that, they are a great way to visually check the refrigerant charge on any system along with any moisture issues. Although charging by superheat on cap tubes in the best way, second to weighing in the charge, I don't think charging a system by superheat, let alone sub-cooling is the correct way either. What is the correct way? By using the recommended refrigerant charge on the piece of equipment. If no tag is available, then I usually just let the system equalize after a recovery, pressurization, deep vacuum and let the refrigerant fly in under pressure until equalization occurs. You will be pretty close to a full charge. As far as sightglasses on ice machine, I recommend installing them for moisture indication purposes and a quick visual check of a refrigerant charge. MOST of the time, a clear glass is a full or overcharged system.
    I never see a sight glass on cap tubes , i usually have to bring out the crystal ball
    Smart man
    Jul 2011
    Lehigh Valley, PA
    Crystal ball? What's wrong, don't you have x-ray vision?
    May 2003
    Utah
    Quote Originally Posted by marter View Post
    Got the box to 42° with a 20° superheat and then box was down to 38° when I left.
    Ive always been told to keep a full glass to ensure all liquid to txv. Manager says to charge to the correct superheat and not worry how full the glass is and coworker says only with R22 you should charge to a full glass
    Your statements here raise a few questions:
    Did you charge to a full sight glass, or charge to superheat as your boss requires?
    In either case, why was the system operating with 20 deg superheat?
    What does your boss want the SH to be?
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by bunny View Post
    In additon are you talking evap SH or pump SH?
    In my opinion, especially on TXV systems, you do not charge by superheat. Only on cap tube systems as a verification after weighing in the charge. I do not see the reasoning that you dont clear a sight glass if the system is R22? If the system is designed properly you should always clear the sight glass unless you exceed 300 pounds of head pressure on R22. If you overcharge the system you may have a pumpdown capacity issue and may go off on high headpressure. Superheat is obtsined by a metering device such as a cap tube or TXV etc. Saying not to clear the sightglass or charging to 20 degrees of superheat is like saying fill your gas tank of your car and stop filling it when you reach 40mpg.......,,kind of........,
    Mar 2009
    Mid-Mo
    This time of the year without a headmaster is hard to get a fan cycling control to level out and get a true solid column of liquid without blocking off the condenser.
    Jan 2013
    Northern CA
    Clear the sight glass, if it has a pump down make sure when it pumps down your not over charged, that's it!
    First off, fan cycling is a very poor method to control head pressure.
    The wide pressure swings cause problems with the TEV operation.
    The TEV not only needs a solid column of liquid (which fan cycling is often hard put to provide) but also wants a steady quality of liquid entering it. If that varies a lot, you'll get poor superheat control.
    Best option on smaller equipment is a headmaster valve. Next option is a combination of ORI/ORD valves.
    As these valves flood the condenser as ambients decrease to maintain proper head pressure, it is vital to have a proper charge in the system so that there is enough refrigerant in the system to fill the condenser at the lowest ambient AND continue to provide liquid to the TEV.
    The easiest way to do this that I've found is by computing the charge required using Sporlan's 90-30-1 chart.
    http://www.sporlanonline.com/90-30-1.htm