Results 14 to 26 of 28
Thread: Proper cfm
-
02-10-2013, 07:47 PM #14
What blower/furnace is it, and what model coil.
-
02-10-2013, 08:17 PM #15
-
02-10-2013, 08:55 PM #16
Professional Member
- Join Date
- Nov 2010
- Location
- kentucky
- Posts
- 161
York air handler md.# AHE30B3XH21A with X13 motor. At the time I ran my test air conditioner was not running and had not been running for days prior. Since I was not familar with the X13 motor I pulled outdoor disconnect at heat pump & made a call for cooling, obtained total cfm on all supplies. A week later I conducted same test after AC had been running for a couple days, hence the lower total cfm.
-
02-10-2013, 09:16 PM #17
An AHE30B can't move 1200 CFM at a .1" ESP. I think your CFM check dry coil was way off.
-
02-13-2013, 05:24 PM #18
Regular Guest
- Join Date
- Feb 2013
- Location
- New Jersey before and after Texas
- Posts
- 51
Is your coil oversized to the blower?
-
02-13-2013, 05:29 PM #19
Regular Guest
- Join Date
- Feb 2013
- Location
- New Jersey before and after Texas
- Posts
- 51
Perhaps you are getting very low temps through the coil causing the air to be way off of .0075.. (I am being a smart ass here). All seriousness with all joking aside are there dip switches on the board, to select cubic feet per minute in cooling mode verses heat, like carrier infinity logic?
-
02-14-2013, 09:39 AM #20A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii
-
02-14-2013, 04:46 PM #21
Regular Guest
- Join Date
- Feb 2013
- Location
- New Jersey before and after Texas
- Posts
- 51
-
02-14-2013, 04:48 PM #22
Regular Guest
- Join Date
- Feb 2013
- Location
- New Jersey before and after Texas
- Posts
- 51
-
02-14-2013, 07:10 PM #23
Regular Guest
- Join Date
- Jun 2001
- Location
- Oklahoma City
- Posts
- 2,591
3.5 ton with 900CFM isn't uncommon. Oddly a 2 or 2.5 ton system can be hooked to the same ductwork and cool the house just as well with a much lower energy bill.. The larger systems tend to fall short on airflow. Peopel are quick to oversize the units, but not install the appropriate ductwork. When you think about the initial install which is charged to the builder by the ton it makes sense.
-
02-18-2013, 02:58 PM #24
Professional Member
- Join Date
- Feb 2013
- Location
- Soon I will be in NE
- Posts
- 16
I bet the source of the confusion is the way you are doing the math. If you use DB temp drop as the only factor - you will never get an accurate read on the airflow in cooling for 2 reasons.
1) the only time DB gives you a complete picture of heat going into or out of a system is in heating mode. If you try to say '3 tons is 36000 Btu - and my temp drop is 13 deg... that means the air flow is .......' You will be missing about 30-40% or more of the story, because cooling systems extract a lot of latent heat which only shows up with a WB temp difference. After taking WB and DB into and out of the system, you need to convert it to an enthalpy change using a chart, then use an adjusted formula to calculate Airflow.
2) a 3 ton refirgerant system does not always give you a real solid 36000 Btu's. Any refrigerant system will naturally have variations in output based on the Evaporating and condensing temperatures. basically, the closer the pressures are on both sides (high side and low side) the more heat your Refrigerant system will move. This means that just as sticklers will (correctly) insist that I cannot know my 150000 btu furnace is delivering the full amount without a combustion analysis test and tuneup (but the difference is USUALLY not enough to drastically throw off air flow calculations) so too, refrigerant systems are usually in the ball park, but not always. Even if it was working properly - which it may not be - charged properly - usually isn't - it may simply be suffering lower output because of low airflow, or high head pressure.
Have fun measuring your airflow without a flow hood - really that is the only accurate way to do so, but you gotta do what you gotta do.
-
02-24-2013, 12:54 AM #25
The square root of the static pressure x 4005 will give you flow velocity in ft/min. Multiply this by your duct cross sectional area in square ft. and this will give you air flow in cfm
-
02-24-2013, 07:02 PM #26


Reply With Quote