    Dec 2003
    Northern VA
    Trane expert WSHP GEHB048
    Does anyone know the model number of the ZSM with a set point only? Also the main board has only one LED w/ no test pins. Seeing no fan op, steady Green LED.
    There are no occupancy switches on the b-13 digital inputs. Any help is appreciated.
    "Iron sharpeneth iron..."
    Jul 2001
    maryland
    Is it 24v controls or a ZN controller?
    Saving the world...one service call at a time.
    Dec 2003
    Northern VA
    It is Tracer ZN510 or 524 with a baysens 006B ZSM.
    My question is, can I get a list of the current diagnostics thru an LED blinks code or do I have to sic "Rover" on it. The literature on the controller and the unit IOM is vague.
    toledo, ohio
    Depends on which wires are hooked to the 006.. 1&2 are your sensor input 3 is your mode 45678 etc are system faults.. You will get voltage errors on ltb you can read with meter...
    Feb 2013
    corona ca
    check the board incoming and out going voltage disregard the LED
    Feb 2013
    Virginia
    I work for Trane and I work on ZN boards all the time. If you are having problems with ops I would first connect with Rover to see your diag., settings etc. If you dont have Rover I would push the service button for 5 seconds and wait, then push it again and again...this will cycle the unit. Fan, reversing valve, compressor and so on. Hope this helps. GL and be safe!