Results 1 to 11 of 11

Thread: MO99 Retro

  1. #1
    Join Date
    Feb 2012
    Location
    Tyler, Tx
    Posts
    11

    MO99 Retro

    I am about to undertake changing out a 50 ton semi herm compressor on an older Trane self contained, water cooled, DX system that had the compressor short to ground. This did create a massive burnout. I'm thinking of using a R-22 replacement such as MO-99 to go ahead and help customer with the current and future cost. Any experiences or advice in this matter would be appreciated.

  2. #2
    Join Date
    Oct 2004
    Location
    toledo, ohio
    Posts
    47
    Go to Emerson's web site, they have a chart on existing refrigerents and retrofit refrigerents including oil and pt charts...

  3. #3
    Join Date
    Dec 2001
    Location
    Phoenix, Az
    Posts
    1,170
    Using a 22 replacement would be wise. I would suggest changing the oil to poe, flushing the system, and going with 407c. Not sure about Trane, but Copeland only allows M099 to be used with Discus comps.

  4. #4
    Carrier's factory service is advertising that they have a MO99 retrofit program commercial systems, i.e. chillers. I am actually looking for information on this as I have a customer with a 30GT with one circuit flat out of refrigerant & they are requesting a retrofit. The question I have is how the EXV controls will be affected by the blend's glide (if it even will be). There is a slight difference in saturation temp @ given pressure. The other question I have is how the reported 5% capacity drop will affect the superheat reading at the compressor's suction sensor. Does anyone have any information to offer? Carrier service is apparently wanting to keep this as a factory service only retrofit program.

  5. #5
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,507
    You know there is no silver bullet on this issue capacity loss is going to happen. Maybe you should get with your local MO99 rep and see what they can do for you.
    Since its an OTC .

    Quote Originally Posted by mpalmer821 View Post
    Carrier's factory service is advertising that they have a MO99 retrofit program commercial systems, i.e. chillers. I am actually looking for information on this as I have a customer with a 30GT with one circuit flat out of refrigerant & they are requesting a retrofit. The question I have is how the EXV controls will be affected by the blend's glide (if it even will be). There is a slight difference in saturation temp @ given pressure. The other question I have is how the reported 5% capacity drop will affect the superheat reading at the compressor's suction sensor. Does anyone have any information to offer? Carrier service is apparently wanting to keep this as a factory service only retrofit program.

  6. #6
    Join Date
    Nov 2004
    Location
    Western NY
    Posts
    943
    Andy Schoen wrote an unbiased article about MO99 retrofits on the RSES journal, The capacity drop is way more than what Dupont want us to believe, there are also flammability issues, I wouldn't recommend it to any of my customers.
    Dupont is coming out with mickey mouse refrigerants like 1234yf, MO99 etc. trying to make money on new patents, the latest batch seems like a desperation move, poor product followed by a huge marketing campaign, even the car manufacturers are rejecting the 1234yf cause flammability issues. I bet Dupont has pretty good lobbyist in DC.

  7. #7
    Join Date
    Apr 2007
    Location
    uk
    Posts
    157
    Curious as to why Carrier Service US would advise retrofiting a chiller over selling a new chiller it doesn't make sense as here in the UK Dupont drop ins are given a wide berth due to various problems using them.

  8. #8
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,507
    Quote Originally Posted by Gibbo View Post
    Curious as to why Carrier Service US would advise retrofiting a chiller over selling a new chiller it doesn't make sense as here in the UK Dupont drop ins are given a wide berth due to various problems using them.
    Just because.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  9. #9
    Join Date
    Apr 2010
    Location
    Naples,FL
    Posts
    588
    I used mo99 in a walk in beer cooler. The problems noted did not show up in the least. The cooler has been operating without even a hiccup for about 9 months. My company is debating the subject and is gonna rule soon corporate wide on what we will use in the future. My only advice would be to talk with your boss and find out what you want to use and stick with it. If you use 407c and the next guy mo99 and the next nu22 than you will end up with a million refigerants in your truck. Make a policy and stick with it. We may be going to mo99 due to the fact that the chain if stores with rack systems may have us retrofit to it so to keep a constant that's all we will use.

  10. #10
    Join Date
    Apr 2012
    Posts
    14
    The global warming potential of MO99 is much worse than 407C. I am at government facility, and our environmental affairs department would not OK MO99 for that reason, we are using 407C. We have done quite a few retrofits of DX units with 407C with no adverse problems. Head pressures are lower, maybe better for compressors, with no noticeable loss in cooling. Copeland is shipping R22 compressor with POE in them, our supplier was able to find them and they are now stocking them. There are some good case sturies at both "Dupont" (MO99)and "National Refrigerants" (407C) web sites

  11. #11
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,157
    Quote Originally Posted by valdelocc View Post
    Andy Schoen wrote an unbiased article about MO99 retrofits on the RSES journal, The capacity drop is way more than what Dupont want us to believe, there are also flammability issues, I wouldn't recommend it to any of my customers.
    Dupont is coming out with mickey mouse refrigerants like 1234yf, MO99 etc. trying to make money on new patents, the latest batch seems like a desperation move, poor product followed by a huge marketing campaign, even the car manufacturers are rejecting the 1234yf cause flammability issues. I bet Dupont has pretty good lobbyist in DC.
    Do you have this article?

    Sent from my SGH-T999 using Tapatalk 2