    High pressure transducer

    Where do you like to see them installed, hot gas or liquid line?

  2. #2
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    27,224
    Post Likes
    If the purpose is to act as a high pressure safety that opens on rising pressure, the compressor discharge line is where it should go.

    If the purpose is low ambient fan cycling or permission where it closes on a rise in pressure, then it's the liquid line.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  3. #3
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    27,224
    Post Likes
    Let's have all the Pro's post their questions in the Pro forum, too.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  4. #4
    Join Date
    Feb 2005
    Location
    USA
    Posts
    1,060
    Post Likes
    Thread Starter
    Its only used for information, the unit has a HP cutout and separate transducer for condenser fan control.

  5. #5
    Join Date
    Feb 2012
    Posts
    32
    Post Likes
    Either where you removed the old one from or discharge, high pressure gas pipe. It seems to cause less problems when you need to remove it from there, in the future.

  6. #6
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,867
    Post Likes
    If it is for building automation, i would prefer the discharge gas line. It would provide more accurate conditions than the liquid line.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  7. #7
    Join Date
    Feb 2005
    Location
    USA
    Posts
    1,060
    Post Likes
    Thread Starter
    Quote Originally Posted by jayguy View Post
    If it is for building automation, i would prefer the discharge gas line. It would provide more accurate conditions than the liquid line.
    Not used for automation, it only used in a display that does absolutely nothing.


    BTW, they put the Penn VFD transducers in the hot gas line, high pressure cut out is in the liquid line.

  8. #8
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    3,661
    Post Likes
    So. You're just using this post as a poll to prove that your customer or controls guy is wrong?

    I think If you had 5 controls guys in a room, and asked them this same question, you'd get at Least 50 different answers.

  9. #9
    Join Date
    Feb 2005
    Location
    USA
    Posts
    1,060
    Post Likes
    Thread Starter
    Quote Originally Posted by 71CHOPS View Post
    So. You're just using this post as a poll to prove that your customer or controls guy is wrong?

    I think If you had 5 controls guys in a room, and asked them this same question, you'd get at Least 50 different answers.
    Where should I send the chicken dinner?

  10. #10
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    27,224
    Post Likes
    Quote Originally Posted by jimp View Post
    Not used for automation, it only used in a display that does absolutely nothing.


    BTW, they put the Penn VFD transducers in the hot gas line, high pressure cut out is in the liquid line.
    If it does nothing, then it is just a matter of the pressure you want to read. If you want to know the pressure in the discharge line, put it there....etc.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules: