Its the LX series and its only a 3Ton so it just have the demand defrost board on it.
The affinity series are the ones with the York guard board on it and the 5Ton LX series has it also.
-
02-09-2013, 09:31 PM #15
Regular Guest
- Join Date
- Jun 2001
- Location
- Moore, Oklahoma
- Posts
- 2,594
You could "split" the W1 and W2 if your air handler has 2 W inputs. Hook W1 to thermostat W output. Connect W2 in air handler to W from defrost board. Connect 10 minute delay on make timer between W1 and W2 if both sets of heat strips are need to be energized by thermostat at design conditions. This configuration with 1/2 the wattage used by the heat strips during normal operating conditions.
-
03-13-2013, 01:14 PM #16
Regular Guest
- Join Date
- Nov 2008
- Location
- New Brunswick, Canada
- Posts
- 18
That is a very good idea. I will actually try that the next time we hook up a LX series York.