I was just wondering if there is anyway on the Honeywell Vision Pro 8000 t-stat to set it up so that the electric doesn't come on so quick? I know on the Honeywell Prestige 2.0 you can set the differential on the electric heat. I have been setting them up with a outdoor sensor to set the LTCO and the BP.
Thanks
-
02-07-2013, 07:24 PM #2
Professional Member
- Join Date
- Nov 2012
- Location
- PA
- Posts
- 40
I called honeywell last week and ask the same question. In short the answer is no. The t'stat adapts to differing conditions such as run time, cycles, and tempatures. The same thermostat hooked to the same type of system in differant houses will turn on aux. heat at differant times. Changing the cycle rates in the installer set up will change when the aux. heat comes on, but there is no setting of time or tempature. Hope this helps.
-
02-07-2013, 07:29 PM #3
Regular Guest
- Join Date
- Jun 2001
- Location
- Oklahoma City
- Posts
- 2,588
Not sure what you are trying to accomplish that setting the LTCO and the BP doesn't already do. If you are close to BP are you wanting there to be a delay for the heat strips coming on?
-
02-07-2013, 07:43 PM #4
You could try turning off that "adaptive intelligent recovery" setting.
That may standardize the run times for each operation mode.
Perhaps you could add a delay-on-make relay that is triggered by a call for heat, but controls the aux. heat circuit.
You'd lose some measure of control, especially in really cold conditions though.
-
02-08-2013, 06:15 AM #5
-
02-08-2013, 05:12 PM #6
Regular Guest
- Join Date
- Nov 2008
- Location
- New Brunswick, Canada
- Posts
- 18
Thanks for the reply's. What i'm looking to do is just not have the AUX kick on so quick. We install York heat pumps and York has come out with there own stat. On that stat I can set the differential between 1st stage 2nd stage and 3rd stage. I just feel like it helps out with the customers power bills thats all.
-
02-08-2013, 05:14 PM #7
Regular Guest
- Join Date
- Nov 2008
- Location
- New Brunswick, Canada
- Posts
- 18
-
02-08-2013, 05:37 PM #8
Setting the auX CPH lower will increase its off time, and on time. Setting the heat pumps CPH higher will decrease how often teh aux comes on.
-
02-09-2013, 04:56 PM #9
The inability to adjust the temperature variance on the auxiliary heat is one reason why I no longer install Honeywell thermostats.
I called them too,close to a year ago, with this issue and was told we are sorry for the inconvenience...
Well, the inconvenience is two fold:
One: You install a new high efficiency system for a customer,( telling them it will save them energy usage) ,only to get a call back 2 months later with the customer saying that their bill is higher than normal during winter.
Two: Once at the residence I find a Honeywell installed, I have to tell the customer "The only way to repair this issue is to buy another new thermostat and have it installed".
This all leaves a bad taste in the customers mouth wondering,"Why didn't you install the most energy efficient thermostat with my new high efficiency unit?"
-
02-09-2013, 05:11 PM #10
Have you set a balance point to lock out aux in warmer temps? It doesn't specifically answer your question but will go a long way for energy savings. Either with an outdoor sensor on the vision pro, or on many york heat pumps with demand defrost you can run "W" thorough the defrost board and lock it out that way - there is a balance point setting on the the board.
Also, I kind of like the delay on make timer in series between the t-stat and the board on the AHU - set to 5 or 10 minutes, experiment a little. Just make sure you don't put the delay on for aux heat during defrost.
Just remember though that less energy consumption always equals less comfort. If you don't run the heaters it will take you longer to get warm. period.
-
02-09-2013, 06:35 PM #11
Regular Guest
- Join Date
- Nov 2008
- Location
- New Brunswick, Canada
- Posts
- 18
-
02-09-2013, 06:38 PM #12
Regular Guest
- Join Date
- Nov 2008
- Location
- New Brunswick, Canada
- Posts
- 18
Yes I have set the balance point on this system, the lowest you can set it is 4.5C. I find it helps out but I feel like I can get a little more out of the heat pump at a little colder temps. The York heat pumps are nice being able to run "W" through the outdoor board.
I may try the delay on make timer just to see what I can get out of these systems.
Thanks for the comments.
-
02-09-2013, 06:48 PM #13
What model is the heat pump. if it has a York guard defrost board. It can be ued to hold out the aux heat.