    medium temp walk in freezing product

    looked at a medium temp walk in today running to cold. found it was getting to about 30 degrees. has a johnson control a419 temp control. checked it against my fluke 52 digital. it seems to be reading about 5-6 degrees off actual temp. ohmed out sensor per manual. got 900 ohms at 40 degrees. right on spec. so i guess that means temp control is bad? sensor ohms correct but temp control reads 44 when actual temp is about 38. box about 10 yrs old, sensor never moved or anything like that.

    also low suction(35 psi with r22) at 35 deg. box, while very low sh, about 1-3 degrees. sight glass clear, fans both on, im thinking coil must be dirty inside restricting airflow. any help appreciated. thanks

  2. #2
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,595
    Ya the suction pressure seems a bit low, but it seems like you are on the right track to me with the cold control. Are you planning on just replacing it or so you want to try to make this one work? If so it's time to put your warm clothes on and adjust it like you would a manual one by waiting on it to make setpoint.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,567

  4. #4
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,585
    Sounds like you're on the right track. Check the settings and dip switches on the a419 before you condemn it. Lock out the new control or the reprogramed control, whichever you find it to be. Is the box cycling on it's own from the control? Is there a chance of a sticking solenoid?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  5. #5
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    727
    ya -all for changing it out, just haven't worked with the a419 much, and want to diagnose it right. like i say sensor ohmed right, but sensed temp is off about 5-6 degrees. there is no re-calibration or anything is there?

    it does cut in and out correct -example i set to 40 with a 4 degree diff. it came on at 40, off right at 35. Its just actual temps were 35-29.

  6. #6
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,595
    Quote Originally Posted by kklobas View Post
    ya -all for changing it out, just haven't worked with the a419 much, and want to diagnose it right. like i say sensor ohmed right, but sensed temp is off about 5-6 degrees. there is no re-calibration or anything is there?

    it does cut in and out correct -example i set to 40 with a 4 degree diff. it came on at 40, off right at 35. Its just actual temps were 35-29.

    If it is set for 40, then it would shut off at 40 then back on at 44.

  7. #7
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    727
    yes comp. does cycle on and off, relay light on control goes on/off, just abou 5-6 degrees off.

    on a separate note the low pressure, with very low superheat could only be lack of airflow correct? i'm thinking coil packed with crud inside? had to leave before they would let me clean it properly.

  8. #8
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    727
    ryan- cut in was 40 with a 4 degree diff.

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,567
    Quote Originally Posted by kklobas View Post
    on a separate note the low pressure, with very low superheat could only be lack of airflow correct? i'm thinking coil packed with crud inside? had to leave before they would let me clean it properly.
    *assuming* a draw-though type evaporator...

    Feel airflow coming out of the fans. If it is coming straight out, then your coil is likely clean.

    If it is coming out at an angle, then you needs to clean it.

  10. #10
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,877
    Quote Originally Posted by ryan1088 View Post
    If it is set for 40, then it would shut off at 40 then back on at 44.
    I think there's some jumpers on it that you can have it cut-in at set point or cut out at set point. Take your pick!

  11. #11
    Join Date
    Aug 2007
    Location
    Southern,Ca
    Posts
    510
    This may be a stupid question but are you sure that the sensor is not located too close to the coil? Where is it located, I like them on the back wall behind the coil mounted on the wall but not touching it..

  12. #12
    Join Date
    Aug 2007
    Location
    Southern,Ca
    Posts
    510
    Quote Originally Posted by KB Cool View Post
    I think there's some jumpers on it that you can have it cut-in at set point or cut out at set point. Take your pick!
    Yes those jumpers do exist, I found them the hard way... I couldnt figure out why the control was cutting in when it should cut out, I figured it out eventually,

  13. #13
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    727
    yes on jumpers. sensor on back wall behind coil, about 2 feet away. it does touch wall, but hasn't been messed with in years. Does it sound like time for a new control or is there any testing left to do. thanks for all the suggestions

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event