Thread: Trane heat pump not defrosting

  1. #1
    Join Date
    Feb 2013
    Posts
    3
    Post Likes

    Trane heat pump not defrosting

    Thanks for your work. I have a Trane XL15i Model 41XW5038A1000BA installed last year. We live at 3500 feet with lots of snow. Have had a severe frosting problem this winter. Cut J2 jumper (per my installer) which increases defrost cutoff temp from 47 to 70 degrees, and defrost every 3 hours for 12 minutes when ambient temp less than 30. Works perfectly and no increase in KWH use compared to before jumper cut. Default is defrost to 47 degrees when ambient temp >30, regardless of whether J2 is cut. In AM when ambient temp >30 unit is heavily frosted. Per manual and discussion with installer have jumped TST to Test Common briefly to increase board timings, then jumped test common to FRC-DFT and unit defrosts. Installer changed defrost board and put in new sensors, checked charge and system operation and said there is really nothing else to do except manually defrost at the defrost board (turning on the cooling cycle at the thermostat also works, and does not turn on the resistance heater which is normally turned on to keep the house warm during the autodefrost cycle). Cools the house a little but works. I don't think the defrost cycle stays on long enough when ambient temp >30. Any suggestions how to proceed? I am not a DIY on this.

  2. #2
    Join Date
    Aug 2010
    Location
    West Monroe, LA
    Posts
    1,594
    Post Likes
    Why is your installer asking you to cut wires etc... On the system? He installed it so he sould be doing all the repairs not you!

    This would be like me buying a new car then calling the dealership to report a problem and them telling me how to fix! That just doesn't make since to me? As far as DIY, although you stated you were not, you are once you started making repairs/cut wires on you system. So we can't offer advice to you. Your installer should be doing this work not you.

  3. #3
    Join Date
    Feb 2013
    Posts
    3
    Post Likes
    Thread Starter
    I don't think following installers instructions qualifies as DYI!

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I think you need another contractor who actually works on heat pumps. Not just sell and install them.

  5. #5
    Join Date
    Feb 2013
    Posts
    3
    Post Likes
    Thread Starter
    He is the local rep in business here for many years. You may not be familiar with this heat pump, as judged by the comments. The installation manual recommends cutting jumper J2 if there is a defrosting problem. It just cycles the defrost every 3 hours for 12 minutes rather than using the sensor, and increasing the defrost cutoff temp from 47 to 70 degrees when ambient temp is less than 30. Otherwise when ambient temp>30 operates in the usual manner with cutoff temp 47. Read the manual.

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Local rep? As he works for Trane. Or just the local dealer. There is a BIG difference.

  7. #7
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    just because its heavy frosted may not be a problem if you let it run how long till it does defrost . when was the last time the coil was cleaned

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •