Any idea as to why this furnace would need the flame sensor cleaned or replaced every month?
-
02-07-2013, 07:31 PM #2
Professional Member
- Join Date
- Nov 2012
- Location
- PA
- Posts
- 40
Is the furnace dirty and sucking in a lot of dust? Is there something in the air that could be burning to it? What are you using to clean it with? Don't use sand paper. I just use a small wire brush.
-
02-07-2013, 11:51 PM #3
as other may chime in on, it may be a poor ground.
flame sense happens with/in the ground path.
if it is truly monthly, I would have tried a new flame sensor after the second trip. also, verified ground and maybe new board.If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?feature...&v=2kX_3y3u5Uo
http://www.youtube.com/watch?v=JVAhr4hZDJE
http://www.youtube.com/watch?v=-TC2xTCb_GU
-
02-08-2013, 12:07 AM #4
New Guest
- Join Date
- Jan 2013
- Posts
- 5
I highly doubt it needs a new flame senor, it is probably the method you are using to clean it. Use low abrasive steel wool. (Not sand paper) Also if the furnace is in a laundry room that could be your issue, lent and silicone base fabric softener in the air will coat the sensor. Check for voltage across "c" and neutral, voltage should be 0 if you have a good ground. Flame sensors don't go bad , It is simply a metal rod insulated with porcelain. A clothes hanger could be a flame sensor if you could mount it without grounding it.
-
02-08-2013, 09:03 AM #5
Check the grounding. From the receptacle through your furnace/board/burners. Must have good earth ground.
-
02-08-2013, 09:47 PM #6
Regular Guest
- Join Date
- Jul 2012
- Location
- Cincinnati ohio
- Posts
- 100
-
02-09-2013, 06:51 AM #7
-
02-16-2013, 01:55 PM #8
Professional Member
- Join Date
- Jun 2006
- Posts
- 27
Ive seen this issue a few times with that model. The furnaces I ran into with this issue were almost always located near a laundry area and were just a few years old. I ended up finding out lennox makes an alternative flame sensor for this model that they said is more robust. I cant recall the part number but lennox should be able to help you if you have ruled out ground issues.