Results 1 to 10 of 10
Thread: Trane varitrac III and Jace
02-06-2013, 07:57 PM #1
Professional Member
- Join Date
- Jan 2008
- Location
- Near Philly
- Posts
- 382
It's been a couple years since my last attempt at this. It was a total disaster last time, was wondering if any improvements with newer revisions to each component. I used the Trane LNML file provided by Tridium last time, all I got was a bunch of unusable data. Any input appreciated.
02-07-2013, 02:57 AM #2
CCPIII was never intended for integration!
02-08-2013, 07:30 PM #3
Professional Member
- Join Date
- Mar 2005
- Location
- Georgia
- Posts
- 328
02-08-2013, 08:08 PM #4
Professional Member
- Join Date
- Jan 2008
- Location
- Near Philly
- Posts
- 382
02-08-2013, 09:39 PM #5
02-08-2013, 10:08 PM #6
Professional Member
- Join Date
- Jan 2008
- Location
- Near Philly
- Posts
- 382
What does that mean? It's 2013 not 2003. The Reliatell unit controller was never intended for integration either. Guess what, I can purchase a LON board or a BACnet board for it today. Why not do the same for the CCPIII. Just rip me off like Trane does with everything else and let me pass onto the end user.
02-09-2013, 12:54 PM #7
#1-cool your jets
#2-think about what you just said, if you can get a LON board for the unit then it WAS intended for integration.
#3-Trane does not offer a LON or BACnet option for the CCPIII because it's firmware/hardware does not support them because...drum roll please....IT WAS NEVER INTENDED FOR INTEGRATION!!!!!!!!
#4-That's what it means.
02-09-2013, 05:58 PM #8
Thank You mallron
04-26-2013, 11:10 PM #9
Professional Member
- Join Date
- Oct 2005
- Posts
- 309
Can't you eliminate the CCP and just bring the dampers and RTU into the Jace via Lon if Comm5 or a driver if Comm4? And can anyone tell me when Varitrac became Comm 5 instead of Comm 4?
05-10-2013, 10:29 PM #10
Varitrac isn't (comm5) or Lon the interface between the Tracker and Varitrac is Lon and any other devices outside of the Varitrac system are also Lon ie: other stand alone rtu's, mp503's, and so on.