    Trane varitrac III and Jace

    It's been a couple years since my last attempt at this. It was a total disaster last time, was wondering if any improvements with newer revisions to each component. I used the Trane LNML file provided by Tridium last time, all I got was a bunch of unusable data. Any input appreciated.

  2. #2
    Join Date
    Apr 2005
    Location
    Boulder,CO.
    Posts
    540
    CCPIII was never intended for integration!

  3. #3
    Join Date
    Mar 2005
    Location
    Georgia
    Posts
    328
    Quote Originally Posted by controldude View Post
    CCPIII was never intended for integration!
    And that is a sham, because it is a pretty good zone control panel. Way to go Trane!

  4. #4
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    382
    Quote Originally Posted by controldude View Post
    CCPIII was never intended for integration!
    No integration = no CCPIII. That's the building owner, can't blame him.

  5. #5
    Join Date
    Jul 2001
    Location
    maryland
    Posts
    1,315
    Quote Originally Posted by mechdorn View Post
    No integration = no CCPIII. That's the building owner, can't blame him.
    That's cool, but the VAV's were never intended for integration either.
    Saving the world...one service call at a time.

  6. #6
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    382
    Quote Originally Posted by mallron View Post
    never intended for integration either.
    What does that mean? It's 2013 not 2003. The Reliatell unit controller was never intended for integration either. Guess what, I can purchase a LON board or a BACnet board for it today. Why not do the same for the CCPIII. Just rip me off like Trane does with everything else and let me pass onto the end user.

  7. #7
    Join Date
    Jul 2001
    Location
    maryland
    Posts
    1,315
    Quote Originally Posted by mechdorn View Post
    What does that mean? It's 2013 not 2003. The Reliatell unit controller was never intended for integration either. Guess what, I can purchase a LON board or a BACnet board for it today. Why not do the same for the CCPIII. Just rip me off like Trane does with everything else and let me pass onto the end user.
    #1-cool your jets

    #2-think about what you just said, if you can get a LON board for the unit then it WAS intended for integration.

    #3-Trane does not offer a LON or BACnet option for the CCPIII because it's firmware/hardware does not support them because...drum roll please....IT WAS NEVER INTENDED FOR INTEGRATION!!!!!!!!

    #4-That's what it means.

  8. #8
    Join Date
    Apr 2005
    Location
    Boulder,CO.
    Posts
    540
    Thank You mallron

  9. #9
    Join Date
    Oct 2005
    Posts
    309
    Can't you eliminate the CCP and just bring the dampers and RTU into the Jace via Lon if Comm5 or a driver if Comm4? And can anyone tell me when Varitrac became Comm 5 instead of Comm 4?

  10. #10
    Join Date
    Apr 2005
    Location
    Boulder,CO.
    Posts
    540
    Varitrac isn't (comm5) or Lon the interface between the Tracker and Varitrac is Lon and any other devices outside of the Varitrac system are also Lon ie: other stand alone rtu's, mp503's, and so on.