Please help -- something wrong with the furnace blow motor?
About a month ago, a contractor came in and replaced the blow motor because hot air was not coming out of the vents. It costs me a fortune, but I was glad my house was warm again. However, I started to feel the temperature in my house is uneven, and the furnace is on more often than before. I only found out yesterday the hot air is coming out only in several rooms, not the others. (same location on both floors) That explains why the furnace was on more because the living room with thermostat has little hot air coming out.
I wonder if it is the issue with the newly installed blow motor, and should I call the contractor to check? On the other hand, I really don't want to spend more money on a 20+ year old furnace. I am thinking about replacing it, but feel bad that I just put in $+ for a new blow motor. Any suggestion? Should this be covered for free by the contractor who installed the blow motor in the first place?
Thank you so much.Last edited by beenthere; 03-13-2013 at 05:47 AM. Reason: Price
-
03-13-2013, 07:31 AM #2
Professional Member*
- Join Date
- Jul 2010
- Location
- nebraska
- Posts
- 1,165
Call and ask for a service manager. He can tell you if there will be a cost or not. I would not have advised to put a fortune in a 20 year old furnace to begin with.
-
03-13-2013, 08:36 AM #3
Regular Guest
- Join Date
- Feb 2006
- Posts
- 19
Thanks, will try. If I decide to replace the furnace, by any chance is the contractor willing to take back the newly installed blower motor at a discounted price? I'd think they can put it to use easily somewhere else? (Sorry if this question is duplicate. I thought I have posted it earlier, but didn't see it yet)
-
03-13-2013, 08:44 AM #4
Is the air coming out as strong as it was before on the registers that it is coming out of? Is there any air at all coming out of the other registers? Could it be that the furnace is moving less air? Do you have a zone system?
-
03-13-2013, 09:22 AM #5
Regular Guest
- Join Date
- Feb 2006
- Posts
- 19
good point. I do feel the air coming out is not as strong as before even for those working registers. For the non-working ones, I can barely feel any hot air. I do have a zone system, but I have't touched it for a long time. Also, I thought zone is per floor,but in my case, the same vertical locations on both floors have the same problem. For example, the living room and the bedroom right above it have no hot air.
Is it a symptom of dying furnace? but before the blower motor incident, everything was fine.
-
03-13-2013, 09:34 AM #6
It might be a simple speed adjustment on the motor no big deal just call the guy back, if not than I would let it ride until you can afford to replace the furnace.
Certified parts changer.
-
03-13-2013, 09:48 AM #7
Regular Guest
- Join Date
- Feb 2006
- Posts
- 19
Thanks. That sounds an easy and quick fix if they don't charge me any more money.
Also, does anybody has any opinion or experience on the contractor taking back the motor say if I go with them to replace the furnace?
-
03-13-2013, 10:07 AM #8
Yea if he charges you more for the furnace than deducts it because there is not a market for used motors and I am sure he gave you the replacement option.
Certified parts changer.
-
03-13-2013, 10:09 AM #9
Professional Member*
- Join Date
- Jul 2000
- Location
- Northern Wisconsin
- Posts
- 1,566
Part of a new blower motor installation should have included the tech measuring the temperature rise across the furnace to make sure that it was within the specifications of that type of furnace. That being said, the old motor may have been adjusted outside of it's safe operating range to "fix" a poor circulation condition that might now be showing itself again. A lot of variables could be the root cause.
Call them back and explain what is the situation since they were there and ask them what they can do for you. Every company will have their own unique set of circumstances in which they'll come back without charging.
As for a refund or discount towards a new furnace.... again that's going to be up to their policy.
First you need to find out why the replacing of a blower motor unbalanced the heating of your home though. This could be an indication of either something really simple or something more substantial. Blower motors don't last forever, but a bad air distribution system can drastically shorten their life.Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.
-
03-13-2013, 10:32 AM #10
I would call and tell them what problems you are having since their repair. The problem may be related, it may not. If it is related it should be no cost, if not get a estimate before they start. Also remember it may be a problem that is not directly related, ie the motor is running perfectly but the tech accidentally caused a problem with the zone system for instance.
I may have missed it but how long has it been since the origional repair, a couple days, weeks, a month, longer? The answer to this question will have a direct affect on how the service company responds.
With the info given I don't think that "this" would be an issue to replace the furnace, but there may be other reasons such as efficiency, safety, age,etc.
-
03-13-2013, 10:34 AM #11
If the company is reputable, they will not sell used parts. Do not expect to get any money back for that motor.
Did they give you a replacement option at the same time as the repair price? Why would you put an expensive motor into a 20 year old furnace?How tall are you Private???!!!!
-
03-13-2013, 10:52 AM #12
Regular Guest
- Join Date
- Feb 2006
- Posts
- 19
Thanks for all the reply. Greatly appreciate it. Let me answer two questions being asked.
I went for the motor replacement because it was the second day since the motor stopped working, and I desperately need the heat back 6pm that day. Didn't want another night without much heat. The tech did mention replacement, but has to be the next day before he can give me a quote.
The blower motor service was done about a month ago. What I have been noticing is that the furnace is on longer and more frequently than before, maybe some uneven temperature inside the house, but I didn't realize some of the registers are cold (living room and one bedroom upstairs, no one lives in that bedroom) until yesterday. It is obvious I am not good at this.
I will call and update what I get back from the contractor.
-
03-13-2013, 11:02 AM #13
I think you just noticed problems that already existed before the motor was replaced. Once the work was done you started feeling around but now it is putting the cart before the horse. With that the tech should have looked into the attic and at least ensured proper air flow.
Certified parts changer.