    I have several vav's that go into auto zero calibration at night and lock themselves "on" in hand. Tried to lock vav's "off" in hand. They do go off but won't lock in hand "off" instead go auto off. The next morning they agin they are locked in hand "on." The point or program that controls this says "Waiting" any ideas.

  2. #2
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    1,401
    More info needed: What brand/model "VAV" controller are you working with ? What kind of supervisory device is running them ?
    If sense were so common everyone would have it !

    All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!

  3. #3
    Join Date
    Aug 2012
    Location
    Phoenix, AZ
    Posts
    16
    Quote Originally Posted by Cagey57 View Post
    More info needed: What brand/model "VAV" controller are you working with ? What kind of supervisory device is running them ?
    what is in hand?

  4. #4
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,092
    Quote Originally Posted by jaceski View Post
    what is in hand?
    Well it could be a cup of Coffee, preferably a quad shot Vinte Vanilla Latte from Starbucks or a bottle of water or a V8 or even a bud light?

    And yes I am wondering the same as you

  5. #5
    Join Date
    Feb 2013
    Posts
    7
    The supervisory device:
    Vendor-Delta Controls
    Model- DSC1616E
    Platform- System
    Version- 3.30
    The VAV:
    Model-DVC-304
    Version-3.30
    Hope this is enough info. Thanks for your response.

  6. #6
    Join Date
    Feb 2013
    Posts
    7
    Definitely have the quad. Shot in hand!!!!!!

  7. #7
    Join Date
    Feb 2013
    Posts
    7
    The supervisory device:
    Vendor-Delta Controls
    Model- DSC1616E
    Platform- System
    Version- 3.30
    The VAV:
    Model-DVC-304
    Version-3.30
    Hope this is enough info. Thanks for your response.

  8. #8
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    1,377
    "Waiting" indicates that the program is being enabled/disabled from another program and does not continuously run.
    As the DVC is a fully programmable controller, the issue could be a number of things that the programmer missed or did not account for.
    More then likely the program calls the auto-calibration mode program and then stops it before the auto-calibration mode is turned off.
    Contact your installing contractor.

    kontrol out
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE

  9. #9
    Join Date
    Feb 2013
    Posts
    7
    The fix! Dropped program of problem VAV and replaced with working VAV program. Imputing critical info: duct size, cfm, sensor type, damper rotation, ect. Time consuming but works.

  10. #10
    Join Date
    Feb 2013
    Posts
    7
    Time for my weekend. Whiskey in "hand". Preferably #Jameson