Results 1 to 10 of 10
    Feb 2013
    Auto zero calibration
    I have several vav's that go into auto zero calibration at night and lock themselves "on" in hand. Tried to lock vav's "off" in hand. They do go off but won't lock in hand "off" instead go auto off. The next morning they agin they are locked in hand "on." The point or program that controls this says "Waiting" any ideas.
    Mar 2009
    Several Miles from Sane
    More info needed: What brand/model "VAV" controller are you working with ? What kind of supervisory device is running them ?
    If sense were so common everyone would have it !
    All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!
    Aug 2012
    Phoenix, AZ
    Quote Originally Posted by Cagey57 View Post
    what is in hand?
    Mount Airy, MD
    Quote Originally Posted by jaceski View Post
    what is in hand?
    Well it could be a cup of Coffee, preferably a quad shot Vinte Vanilla Latte from Starbucks or a bottle of water or a V8 or even a bud light?
    And yes I am wondering the same as you
    Feb 2013
    The supervisory device:
    Vendor-Delta Controls
    Model- DSC1616E
    Platform- System
    Version- 3.30
    The VAV:
    Model-DVC-304
    Version-3.30
    Hope this is enough info. Thanks for your response.
    Feb 2013
    Definitely have the quad. Shot in hand!!!!!!
    Feb 2013
    Model- DSC1616E
    Platform- System
    Version- 3.30
    The VAV:
    Model-DVC-304
    Version-3.30
    Dec 2006
    What? Who? Where?
    "Waiting" indicates that the program is being enabled/disabled from another program and does not continuously run.
    As the DVC is a fully programmable controller, the issue could be a number of things that the programmer missed or did not account for.
    More then likely the program calls the auto-calibration mode program and then stops it before the auto-calibration mode is turned off.
    Contact your installing contractor.
    kontrol out
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE
    Feb 2013
    The fix! Dropped program of problem VAV and replaced with working VAV program. Imputing critical info: duct size, cfm, sensor type, damper rotation, ect. Time consuming but works.
    Feb 2013
    Time for my weekend. Whiskey in "hand". Preferably #Jameson