I have several vav's that go into auto zero calibration at night and lock themselves "on" in hand. Tried to lock vav's "off" in hand. They do go off but won't lock in hand "off" instead go auto off. The next morning they agin they are locked in hand "on." The point or program that controls this says "Waiting" any ideas.
-
02-05-2013, 07:48 PM #2
Professional Member*
- Join Date
- Mar 2009
- Location
- Several Miles from Sane
- Posts
- 1,402
More info needed: What brand/model "VAV" controller are you working with ? What kind of supervisory device is running them ?
If sense were so common everyone would have it !
All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!
-
02-05-2013, 11:16 PM #3
Regular Guest
- Join Date
- Aug 2012
- Location
- Phoenix, AZ
- Posts
- 16
-
02-06-2013, 12:37 AM #4
-
02-09-2013, 01:48 PM #5
Regular Guest
- Join Date
- Feb 2013
- Posts
- 7
The supervisory device:
Vendor-Delta Controls
Model- DSC1616E
Platform- System
Version- 3.30
The VAV:
Model-DVC-304
Version-3.30
Hope this is enough info. Thanks for your response.
-
02-09-2013, 01:49 PM #6
Regular Guest
- Join Date
- Feb 2013
- Posts
- 7
Definitely have the quad. Shot in hand!!!!!!
-
02-09-2013, 10:00 PM #7
Regular Guest
- Join Date
- Feb 2013
- Posts
- 7
The supervisory device:
Vendor-Delta Controls
Model- DSC1616E
Platform- System
Version- 3.30
The VAV:
Model-DVC-304
Version-3.30
Hope this is enough info. Thanks for your response.
-
02-09-2013, 10:09 PM #8
"Waiting" indicates that the program is being enabled/disabled from another program and does not continuously run.
As the DVC is a fully programmable controller, the issue could be a number of things that the programmer missed or did not account for.
More then likely the program calls the auto-calibration mode program and then stops it before the auto-calibration mode is turned off.
Contact your installing contractor.
kontrol out"Can't we all just get a Lon?" - Garry Jack
"BACnet: integration or interrogation?" - The Janitor
"Open protocols? You can't handle open protocols!" - Nathan R. Jessup
“What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE
-
02-13-2013, 10:18 PM #9
Regular Guest
- Join Date
- Feb 2013
- Posts
- 7
The fix! Dropped program of problem VAV and replaced with working VAV program. Imputing critical info: duct size, cfm, sensor type, damper rotation, ect. Time consuming but works.
-