    York 350 ton chiller

    New to the commercial side but need some info, Company I work for just had a compressor replaced on a York screw drive chiller. The york controller has a 2 minute delay after metasys commands start but after the compressor starts there is a 30 minute count down if the compressor should shut down for any reason it will not try a restart until the countdown ends. After the 30 minute delay it reverts back to the 2 minute delay if it shuts down WHY? If its for anti short cycling I would think it would have a longer delay then 2 minutes between off command and restart what difference would a 30 minute run time do

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,878
    Post Likes
    What model?

  3. #3
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    69
    Post Likes
    That is part of prestart , waiting for flow , time for slide valve to zero out . If unit had a oil pump this would be prelube.

  4. #4
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,583
    Post Likes
    Yep, 30 minutes (usually from start to start) is to limit short cycling and two minutes is for pre-start sequence.

  5. #5
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    825
    Post Likes
    Quote Originally Posted by Nuclrchiller View Post
    Yep, 30 minutes (usually from start to start) is to limit short cycling and two minutes is for pre-start sequence.
    x2

    2 mins is for presetting the variable orifice.

    30 mins is anti-recycle

  6. #6
    Join Date
    Jan 2011
    Posts
    1,392
    Post Likes
    Quote Originally Posted by Sicofthis View Post
    x2

    2 mins is for presetting the variable orifice.

    30 mins is anti-recycle
    Really? A variable orifice valve on a screw chiller? I don't think so.

    The 2 minute lock-out is post shutdown, not pre-start. The pre-start is 30 seconds.

    To the original poster...it would behoove you to get a copy of York Form 160.47-O1 and read it. The question you asked is explained on page 7. The manual is available on JCI's website. Do a little digging you'll find it.

  7. #7
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,583
    Post Likes
    Quote Originally Posted by KnewYork View Post

    ...The 2 minute lock-out is post shutdown, not pre-start. The pre-start is 30 seconds...
    I stand corrected.
    Thanks, KnewYork.

    I think the conversation about two timers (and not a third), and how they relate to starting, is what threw me off. Not trying to make excuses, just trying to.... Aw heck! who am I trying to kid? Dang it. What I get for trying to jump in before Jay.

  8. #8
    Join Date
    Sep 2002
    Posts
    14,990
    Post Likes
    The 30 minute post-start interval is to prevent the drive motor from overheating / allow the refrigeration system's operation to dissipate the heat in the windings after a start. Many motors are only rated for a certain number of starts per hour. Usually 2 or 3 in my experience.

    PHM
    ------


    Quote Originally Posted by jnaas2 View Post
    New to the commercial side but need some info, Company I work for just had a compressor replaced on a York screw drive chiller. The york controller has a 2 minute delay after metasys commands start but after the compressor starts there is a 30 minute count down if the compressor should shut down for any reason it will not try a restart until the countdown ends. After the 30 minute delay it reverts back to the 2 minute delay if it shuts down WHY? If its for anti short cycling I would think it would have a longer delay then 2 minutes between off command and restart what difference would a 30 minute run time do
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  9. #9
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    825
    Post Likes
    Quote Originally Posted by KnewYork View Post
    Really? A variable orifice valve on a screw chiller? I don't think so.

    The 2 minute lock-out is post shutdown, not pre-start. The pre-start is 30 seconds.

    To the original poster...it would behoove you to get a copy of York Form 160.47-O1 and read it. The question you asked is explained on page 7. The manual is available on JCI's website. Do a little digging you'll find it.









    Start sequence is 30 secs to 2 mins depending on variable orifice actuator speed.

  10. #10
    Join Date
    Apr 2014
    Location
    Evansville, In
    Posts
    52
    Post Likes
    Thanks for the info gentleman and knewyork ill look that up, Going to Johnson control next week for a little training, cant wait

  11. #11
    Join Date
    Jan 2011
    Posts
    1,392
    Post Likes
    Sicofthis...you are correct if the chiller is a style E. I made the asumption that it was an older style. However, the 2 min. lockout is still a shutdown function not a pre start function.

  12. #12
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    825
    Post Likes
    Quote Originally Posted by KnewYork View Post
    Sicofthis...you are correct if the chiller is a style E. I made the asumption that it was an older style. However, the 2 min. lockout is still a shutdown function not a pre start function.
    agree to disagree


    1) start command sent
    2) preparing to start in *** secs displayed (or something similar)

    *** secs is valve preset time 30 to 120 secs


    too low a preset time will nuisance trip on low oil differential 3 mins after startup expecially with cold condenser water. Too long can trip low evap.

  13. #13
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    69
    Post Likes
    If you go back to single line micro panel of the late 1990 on a YS chiller a two minute timer starts , press stau


    Sent from my iPhone using Tapatalk