    Thoughts on controlling a DX air handler

    We've got this old building we are retrofitting, the existing Trane air handler with 2 Carrier CU's is staying. Don't have M#'s not sure it would matter after 20 years of hackery not much is original anymore anyway. I'm looking for thoughts on the best way to control the DX. Each CU has an O6E I believe and is supposed to get 2 electric unloaders to replace the current mechanical units. We have 2 evaps and LLSV per CU. My thought was to stage cooling up and down via the 4 LLSV's and load/ unload the comps to maintain suction pressure. I'm trying to keep this a simple as possible. Thanks

  2. #2
    Join Date
    Oct 2005
    Location
    B.C. Canada
    Posts
    1,267
    Post Likes
    Sounds like your on the right track, load and unload based on suction, control the llsvs threw relays from the stat

  3. #3
    Join Date
    May 2000
    Location
    Salem, WI US
    Posts
    83
    Post Likes
    Honeywell has a retrofit economizer control that's easy to install, also you may want to consider hot gas bypass depending how low your compressors can unload.

    Beta

  4. #4
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Is this ahu doing ventilation air? Single zone? Multi zone? Trying to just make 55 degree air?

  5. #5
    Join Date
    May 2009
    Location
    in the present
    Posts
    94
    Post Likes
    Thread Starter
    Thanks for the replies, it's a multizone all new VAV's, DAT will be reset based on demand we will control econo also. Hot gas is already piped also not sure it is really needed but I'm sure we will make that work as well.

  6. #6
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    Quote Originally Posted by kirkH View Post
    Thanks for the replies, it's a multizone all new VAV's, DAT will be reset based on demand we will control econo also. Hot gas is already piped also not sure it is really needed but I'm sure we will make that work as well.
    Is there a BAS system controlling the VAV boxes? If so, why not use the BAS system to control the AHU? The only thing different from a built-up system would be the control modulation of the DX system. You will need to insure that the DX system has all the necessary safeties in place and interlocked with control system.
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com

  7. #7
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    We have a few that are setup similar to that. Multi zone air handlers can be a trick though on a dx unit, if you have one zone call for cooling all the time it's possible to keep a call for cooling on for a really long time and run unloaded.

  8. #8
    Join Date
    Oct 2005
    Location
    B.C. Canada
    Posts
    1,267
    Post Likes
    Quote Originally Posted by ryan1088 View Post
    We have a few that are setup similar to that. Multi zone air handlers can be a trick though on a dx unit, if you have one zone call for cooling all the time it's possible to keep a call for cooling on for a really long time and run unloaded.
    Oil return probems? Properly sized double risers should take care of that

  9. #9
    Join Date
    May 2009
    Location
    in the present
    Posts
    94
    Post Likes
    Thread Starter
    Quote Originally Posted by air1 View Post
    Is there a BAS system controlling the VAV boxes? If so, why not use the BAS system to control the AHU? The only thing different from a built-up system would be the control modulation of the DX system. You will need to insure that the DX system has all the necessary safeties in place and interlocked with control system.
    It's all going to be managed by the BAS we are installing, just trying to nail down the best control scheme for the DX.

  10. #10
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    Quote Originally Posted by kirkH View Post
    It's all going to be managed by the BAS we are installing, just trying to nail down the best control scheme for the DX.
    That can be a little tricky. You'll need a PID loop to control the DAT setpoint. The loop output of the DAT PID will stage the DX. The tricky part is the time delays to prevent short cycling of the compressors. If you have a good programer with a solid understanding of DX he/she should be able to figure it out.
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com

  11. #11
    Join Date
    May 2009
    Location
    in the present
    Posts
    94
    Post Likes
    Thread Starter
    Quote Originally Posted by air1 View Post
    If you have a good programer with a solid understanding of DX he/she should be able to figure it out.
    That would be me. After looking at this thing it occurred to me that I never gave much thought into how something like this was being controlled back in the day when I was a service tech. Dusting off some pretty old brain cell on this one.

  12. #12
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by coolerik View Post
    Oil return probems? Properly sized double risers should take care of that
    We lost one compressor to that and being low on charge. The other one that died short cycled so fast that the compressor shorted to ground.

  13. #13
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,426
    Post Likes
    On an old system like this using DAT is not the best. depending on how many zones you are dealing with, i would either use a stat located in a common area or use RAT. and than use reheats in zone dampers. Of course using unloaders along with suction pressure will help. but again not great when humidity comes into play.

    But if your going to use a BAS why not just install zone dampers and bypass.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •