    The inverted loop helps to prevent the liquid refrigerant, that migrates to/condenses in the evaporator coil in the off cycle, from running down the suction line to the compressor on start-up.
    That is the reason pretty much every equipment manufacturer, and piping guide, calls for the inverted loop when the coil is above the outdoor unit.

    As has been pointed out, depending on how the piping inside the coil enclosure is piped from the factory, and the orientation of the coil, the suction line may already be routed higher than the rest of the coil before it even leaves the cabinet.
    I always rout the refrigerant lines up after exiting the cabinet anyway.
    If more government is the answer, then it's a really stupid question.

  2. #28
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,117
    Quote Originally Posted by Cooked View Post
    Nope
    Yep, it does.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #29
    Join Date
    Aug 2011
    Location
    Bangalore
    Posts
    21
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 02-07-2013 at 05:57 AM. Reason: non AOP member

  4. #30
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,685
    jatinder.bhargav

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event