    Jun 2010
    Nelson, Canada
    need Armstrong igniter advice
    Looking at an Armstrong 80 GUJ100D12-2B furnace that's not igniting but I am unfamiliar with the hot surface ignition system. Just trying to determine if it's the gas valve or igniter, What kind of voltage should I be seeing on the igniter leads? I'm getting 6 volts.
    Calgary, Alberta
    Is there a smart valve on that furnace?
    Quote Originally Posted by zacmobile View Post
    With the pilot burner cable connected, and voltage measurements taken while the ignitor is powered, you should have 24 volts.
    Ignitor should ohm out at less than 10 ohms.
    May 2012
    Upper Michigan
    Hey rundawg, do you have any sort of file on ohm reading for different ignitors? I just would like something to save or else I forget.
    I don't have a break down for each and every ignitor on the market, but I sent you an email with what I have.
    The resistance of a Norton silicon igniter used in the Q3450 or Q 3480 pilot assemblies, when new and
    cold, will be between 3 and 4 Ohms (average 3.7 Ohms) as the igniter ages the resistance will increase. When
    its resistance reaches 10 Ohms the igniter should be replaced
    anyone have a better cut & paste about the ignitors
    May 2012
    Upper Michigan
    Quote Originally Posted by rundawg View Post
    Thanks for that, any info I don't have to try to remember is good info lol.
    Jun 2010
    Nelson, Canada
    That helps, thanks guys.