    JCI FX-60 Queue Full Exception

    I am at a new customers site and he has an FX-60 which is performing very poorly. I looked at the station output and see the following:

    javax.baja.util.QueueFullException
    at javax.baja.util.Queue.enqueue(Queue.java)
    at javax.baja.util.CoalesceQueue.enqueue(CoalesceQueu e.java)
    at com.tridium.basicdriver.util.BBasicWorker.post(BBa sicWorker.java)
    at com.tridium.basicdriver.BBasicNetwork.postWrite(BB asicNetwork.java)
    at com.tridium.jcin2.point.BJciN2ProxyExt.write(BJciN 2ProxyExt.java)
    at javax.baja.driver.point.Tuning.write(Tuning.java)
    at javax.baja.driver.point.Tuning.process(Tuning.java )
    at javax.baja.driver.point.BTuningPolicyMap$Backgroun dThread.process(BTuningPolicyMap.java)
    at javax.baja.driver.point.BTuningPolicyMap$Backgroun dThread.run(BTuningPolicyMap.java)

    I saw that the tuning policy was set up with the min/max write times at 0. The stale time is at 0 also. The write on start, write on up and write on enabled are all set to false. Is there any way to find out what is causing this?

    Thanks in advance.

  2. #2
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    1,063
    Post Likes
    Thread Starter
    Update. I went through all 50 controllers on the trunk and found a problem with the VMA's. About 1/2 of the VMA's had points faulted in the FX-60 and upon further investigation, I found that the points didn't exist in the configuration. As soon as I deleted these points ( about 60 total ), the queue errors stopped.