I have an issue with this Rheem unit, I need Ideas of poss solutions..The unit is cooling normally like it should but is blowing water through the coil into the supply duct and leaking inside the house, the drain pan is not leaking I opened one of the covers when it was running and I saw water blowing from the evaporator down to the supply duct. Does humidity make the evap create all that water? or the blower is melting all the frost from the evap coil. I have never seen this !! any ideas? thanks for the help.
-
02-04-2013, 07:49 AM #2
Spray the coil good with a self rinsing cleaner. Could be that oil on it is causing droplets of water to fly off and not do what they are supposed to do in draining.
-
02-04-2013, 10:17 AM #3
Professional Member
- Join Date
- Jul 2007
- Location
- Chicago IL
- Posts
- 165
How much frost are you seeing?
-
02-04-2013, 10:31 AM #4
You may need a trap on your drain line. You can get this problem from dirty filter, dirty coil, poor slope on your drain pan and so on. Just make sure your pan, coil and drain line are clean first. I have had to pull out many Rheem coils to clean the pans.
-
02-04-2013, 10:40 PM #5
New Guest
- Join Date
- Jan 2013
- Posts
- 5
Fenian.. I could not see any frost on the coil, all I could see was water flying off the evap coil, it is blowing cold air. I am going to check what McLean air is saying that makes sense. thank you all for your help
-
02-05-2013, 01:09 AM #6
New Guest
- Join Date
- Jan 2013
- Location
- Missouri
- Posts
- 5
Does it have enough clear airflow through the duct and good supply and return air?
I would suggest taking the evap out to get a good look at it and clean it perhaps use the self rinsing cleanser first as suggested above.
Provided it has a proper trap(not a running trap) and the slope is good, pan, coil and drain line are clean like McLean said, well that would stump me too!
good luck!
-
02-05-2013, 01:32 AM #7
Professional Member
- Join Date
- Oct 2012
- Location
- Sacramento,ca
- Posts
- 172
I this a horizontal unit? And if so what brand of coil is it? All i install is rheem equip with Adp coils and if you dont install the supplied drip pan that attaches to the drainpan to catch water blowing off the coil you will get the issue you are having.
-
02-05-2013, 06:10 AM #8
X2 for drip pan and crappy duct = high static = water in supply duct
-
02-05-2013, 08:56 PM #9
Regular Guest
- Join Date
- Feb 2011
- Posts
- 18
I had a problem like this once before and I had good slope on my pan, pan was clear and free of dirt along the coil. Turns out that the furnace was moving way to much air over the coil. Sounds like you may be moving too much air.
-
02-05-2013, 08:58 PM #10
Regular Guest
- Join Date
- Feb 2011
- Posts
- 18
check your air flow you should be running at about 400 cfm per ton of cooling.
-
02-05-2013, 09:16 PM #11
Regular Guest
- Join Date
- Feb 2013
- Location
- Nashville, TN
- Posts
- 6
Is this an A coil? Ive had one before doing the same thing. that I had to remove the triangle sheet metal on the end of the coil and put some cork insulation tape on the edge and reinstall it and it fixed it. another thought... possible the blow off sheild has fallen down or anything? shouldnt need a p trap unless coil is on negative side of blower.
-
02-05-2013, 09:35 PM #12
-
02-07-2013, 03:05 PM #13
Professional Member*
- Join Date
- Apr 2010
- Location
- NC Sandhills
- Posts
- 191
Is this a new system or an older system that has just started doing this? Heat pump or furnace with coil. I assume its horizontal in attic. It could be alot of things, but the easiet things to try first is clean coil, could be oily or have sediment build up. If coil is fine sounds like to much airflow.