    it will run fine when i am there i run thru 5 or 6 cycles with no problem a couple of hours lator i will get called back blowing cold air ignition failure

  2. #15
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,157
    Check connection at gas valve. Those plugs get loose connections to the point it can be a nuisance indeed and replacing it is the fix. I've had quite a few. Just an idea, which I don't typically offer ideas or instances I've had but since you already replaced a lot of parts . . Just a thought. I'm not a predator fan because they have in what my opinion is minor design issues that effect heating.

    Sent from my SGH-T999 using Tapatalk 2

  3. #16
    Explain more, I am very familiar with gas issues please explain more, what are you seeing, gas pressures? temp rise? etc...

  4. #17
    Join Date
    Nov 2004
    Location
    Western NY
    Posts
    943
    My guess is that the primary limit is tripping after the burners fired for awhile, you are getting flash code 9, right? strap a thermometer to the limit, see if it gets near 190F.

  5. #18
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    2,685
    check resistance thru rollout switch and hall switch. could be one problem.

    also check for wind. these units hate wind.

    and lastly, check pilot flame

  6. #19
    Join Date
    Mar 2013
    Location
    Joplin,Missouri
    Posts
    286
    If you are getting a flash code 9 ignition failure code that can also be an open primary limit check for airflow issues/dirty filters/dirty coil

  7. #20
    Join Date
    May 2010
    Location
    Brooklyn, NY
    Posts
    82
    okay, make sure you are looking at the right PCB, there's one at the burner assembly, if that work has a steady blink, then it's working fine, according to what you say, it might not be ignition failure. Check the main PCB, the place where all the wires are at, see if you get a 9 flash code at the Heat Delay LED, if it does show 9, that means one of the limit is tripped. Now go to the burner compartment, there's a high limit that sticks into the burner, see if that's continuity, most likely it's that place that shows error. And yes, if you restart the power supply, the unit will run fine again for some time. If it does run fine, that means you're not getting enough return air, check the return duct filter etc...