02-08-2013, 05:38 PM #27
-
02-09-2013, 12:09 AM #28
Regular Guest
- Join Date
- Feb 2013
- Posts
- 11
Removed existing wires from gas valve. Used jumper from r and jumper from common. Once board gave call for gv, manually gave gv 24v from terminal block on board.
Not sure if this is a good thing or a bad thing, but it worked. Allowed us to rule out gv and find the real problem. Also able to determine gas pressure.
-
02-09-2013, 12:33 PM #29
I guess it's fine if the GV relay and GV are on their own little circuit. I just grabbed the nearest Carrier schematic I have and it appears the pressure switch has a way back to common thru the CPU, so that unhooking the GV wires would not effect the rest of the cycle. I never bothered to notice whether most furnaces are likewise wired, always assumed all the safeties were wired in series with GV to shut it down if one opened.
-
02-09-2013, 01:55 PM #30
Regular Guest
- Join Date
- Feb 2013
- Posts
- 11
True, on this particular Trane, the board controlled gas valve on its own mini circuit, per the 12 pin plug.
-
02-09-2013, 02:39 PM #31
Great idea, disconnecting existing wiring on the valve and running a 24 and common off the low voltage coming in, basically bypassing the board control, then testing the opening of the valve by the outgoing pressure..Thanks!
-
02-15-2013, 07:48 AM #32
Professional Member
- Join Date
- Feb 2013
- Location
- north georiga
- Posts
- 105
-
02-15-2013, 07:51 AM #33
Professional Member
- Join Date
- Feb 2013
- Location
- north georiga
- Posts
- 105
encountered a similar problem (on an l.p. gas system) and found it to be the second stage regulator locking up as soon as there was a slight drop in pressure,
-
02-15-2013, 07:59 AM #34
could be bad solenoid coil in valve, weak transformer, voltage drop across pressure switch (check w/ volts not continuity), overloaded transformer (disconnect all peripherals and jump unit out at IFC)
-
02-15-2013, 08:01 AM #35
If the PS is in series to the gas valve, then my money would be on a volt or 2 drop across that switch
-
02-16-2013, 01:33 AM #36
New Guest
- Join Date
- Feb 2013
- Posts
- 1
Check if it properly grounded,than check gv valve.
-
02-17-2013, 08:53 AM #37
Professional Member
- Join Date
- Nov 2011
- Location
- Philadelphia, PA
- Posts
- 143
-
02-20-2013, 05:34 PM #38
If if you or anyone else has 10 volts between the neutral and the equipment grounding conductor, you've got some work to do there my friend.
-
02-20-2013, 07:34 PM #39
Professional Member*
- Join Date
- Mar 2001
- Posts
- 1,407
X2
One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........